gets in to do a test on this new hair salon in Leeds today...
there were 3 new circuits to test + one existing for the window lights...metal clad wylex 4 way with BSEN60898s replacing the BS3036s..
anyway....my (R1 R2)`s are going well until it comes to the window lights...theres 10 of em in there...all class 1s and 5 of em had no R2 continuity....
time to open some enclosures i thinks...
and it was like there had been 2 guys connecting up when they were installed....as some of em had continuity...
but 5 were just left unearthed...and no attempt had been made to stab the CPC into the earth box provided...even the earth screw had never been undone...you could just tell.....
odd.....and they will have been like that for at least 15 years...
anyway, all done and safe...:biggrin: