5,382
so..
gets in to do a test on this new hair salon in Leeds today...

there were 3 new circuits to test + one existing for the window lights...metal clad wylex 4 way with BSEN60898s replacing the BS3036s..

anyway....my (R1 R2)`s are going well until it comes to the window lights...theres 10 of em in there...all class 1s and 5 of em had no R2 continuity....
time to open some enclosures i thinks...
and it was like there had been 2 guys connecting up when they were installed....as some of em had continuity...
but 5 were just left unearthed...and no attempt had been made to stab the CPC into the earth box provided...even the earth screw had never been undone...you could just tell.....
odd.....and they will have been like that for at least 15 years...
anyway, all done and safe...:biggrin:
 
But it worked didn't it... I have had this before some people are oblivious to "earth" and what it does..

I remember one DB i quoted for some time ago where they had no CPC in the lights and all 35 fittings (lights / switches) were class one. When I quoted for a partial Rewire she said I was on the make as the lights are perfectly fine and work.
 
I would say the the majority of customers dont understand. I recall failing a periodic a few year ago for no zs on lighting curcuit with class 1 fittings.. When i explained this he replied "Thats rubbish i fitted them lights a few years ago and there was an earth there.. Look ill show you.. Anyway needless to say i didnt get the remidial work.
 

Reply to was it a labourer? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
702
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock