I have just completed an EICR.
One item that I am unsure about is requirements for RCD protection prior to the 17th.
The consumer unit has RCD protection for sockets but not the lights or cooker. New work was carried out in 2006/7 which included lights/extractor fan in the new bathroom and also cables chased into walls <50mm for the cooker circuit. Should this have been RCD protected under the 16th?

Cheers.
 
I think the bathroom lights should have been rcd protected under 16th edition but not sure. But it doesn't really matter when it was done, an EICR is carried out to current standards is it not? Obviously older installations don't meet the requirements of the 17th edition, and come July nothing will meet the requirements of the 18th edition!
 
One item that I am unsure about is requirements for RCD protection prior to the 17th.
The consumer unit has RCD protection for sockets but not the lights or cooker. New work was carried out in 2006/7 which included lights/extractor fan in the new bathroom and also cables chased into walls <50mm for the cooker circuit. Should this have been RCD protected under the 16th?
No, there wasn't any requirement under the 16th Edition. However, it should be remembered that you are not assessing against the requirements of the 16th Edition so that is actually irrelevant. You need to make a judgement on the safety of the installation today, bearing in mind that no additional protection (which incidentally was called supplementary protection under the 16th Edition) by a 30mA RCD where now required MUST be given a coded observation.
 
code appropriately to todays regs, C3 for cables <50mm in wall with no RCD, imo potentially a C2 for those bathroom bits depending which zone they fall in if any.
if fittings are correctly installed they won't fall in anywhere. :D:D
 
Thanks for the replies everyone.

I agree with the majority of you. If RCD protection was not required under the 16th then its a C3 as the regs are not retrospective.
 
Socket outlets were on the rcd side of the split load boards and cookers were as well when they had the isolator with socket on it.
 
Socket outlets were on the rcd side of the split load boards and cookers were as well when they had the isolator with socket on it.
Generally they were, but if I remember correctly under the 16th Edition it stated that RCD protection was required for socket outlets that were reasonably expected to supply outside equipment.
So if you lived in a top floor flat there was no need.
 
I agree with the majority of you. If RCD protection was not required under the 16th then its a C3 as the regs are not retrospective.

The 16th is irrelevant, you inspect and test to the current regulations.

Complying with a previous edition doesn’t necessarily make something non-compliant (for example old wiring colours) but that does not mean that you change your code dependant on when it was installed.
If it requires RCD protection now then it should be coded accordingly regardless of when it was installed.
 
The 16th is irrelevant, you inspect and test to the current regulations.

Complying with a previous edition doesn’t necessarily make something non-compliant (for example old wiring colours) but that does not mean that you change your code dependant on when it was installed.
If it requires RCD protection now then it should be coded accordingly regardless of when it was installed.
Can I make sure I'm understanding you. Are you saying that as soon as the regs change, then if you carry out an EICR then the codes would be related to the current regulations?

For example, 4.4 on the EICR schedule of inspections relates to fire rating of the CU. Nearly all CU's (because they are plastic) will not meet this regulation so will need to be coded accordingly.

In addition, I guess red/black cable could be classed as not being identified correctly so would need to be coded under 5.1 of the schedule of inspections.

There would be many, many more examples. I'm not sure if this is the point you are trying to get across as you are usually right but in this case it seems you are suggesting older properties which met the regulations at the time will be coded if they do not meet current regulations?
 
I would say that you are assessing for safety of continued operation, the guide to this safety is the current edition of the wiring regulations.
However if you assess something that has red and black cables the mere colour of them (which does not meet current regulations) would not be a significant risk and so would not be coded.
If you consider that a plastic CU would present a risk then that may be coded to a level that you consider appropriate to the situation.
 
I would say that you are assessing for safety of continued operation, the guide to this safety is the current edition of the wiring regulations.
However if you assess something that has red and black cables the mere colour of them (which does not meet current regulations) would not be a significant risk and so would not be coded.
If you consider that a plastic CU would present a risk then that may be coded to a level that you consider appropriate to the situation.
When you think about it, the situation of plastic CU's only came about when fuse carriers were replaced by circuit breakers. No high ranking electrical knob had the slightest idea what was going to happen there, did they?

The situation regarding circuit protection should take into account the state of the existing installation. No sign of any danger and been in place for ages, discounting other factors, where's the problem? Attention advised. C3.
 
Can I make sure I'm understanding you. Are you saying that as soon as the regs change, then if you carry out an EICR then the codes would be related to the current regulations?

For example, 4.4 on the EICR schedule of inspections relates to fire rating of the CU. Nearly all CU's (because they are plastic) will not meet this regulation so will need to be coded accordingly.

In addition, I guess red/black cable could be classed as not being identified correctly so would need to be coded under 5.1 of the schedule of inspections.

There would be many, many more examples. I'm not sure if this is the point you are trying to get across as you are usually right but in this case it seems you are suggesting older properties which met the regulations at the time will be coded if they do not meet current regulations?

Yes you inspect and code to the current regulations.
As you already know you only make observations about, and code accordingly, safety related items.

Old colour wiring is not immediately dangerous, is not potentially dangerous, does not attract any recommendation for improvement nor require further investigation therefore no observation is made or code applied.

Yes I am saying that any installation which was installed to previous regulations will have observations made and codes applied to any safety related non-compliance.

The regulations are changed to improve safety and some of the reasons for carrying out an eicr is to ensure its continued safety for use, highlight improvements which could be made in light of advances in technology and regulations and to help bring older installations up to current standards.

Yes this can seem a little over the top in domestic installations, but domestic installations are only a small part of the broad scope of bs7671.
 
Can I make sure I'm understanding you. Are you saying that as soon as the regs change, then if you carry out an EICR then the codes would be related to the current regulations?

For example, 4.4 on the EICR schedule of inspections relates to fire rating of the CU. Nearly all CU's (because they are plastic) will not meet this regulation so will need to be coded accordingly.

In addition, I guess red/black cable could be classed as not being identified correctly so would need to be coded under 5.1 of the schedule of inspections.

There would be many, many more examples. I'm not sure if this is the point you are trying to get across as you are usually right but in this case it seems you are suggesting older properties which met the regulations at the time will be coded if they do not meet current regulations?

Yes you inspect and code to the current regulations.
As you already know you only make observations about, and code accordingly, safety related items.

Old colour wiring is not immediately dangerous, is not potentially dangerous, does not attract any recommendation for improvement nor require further investigation therefore no observation is made or code applied.

Yes I am saying that any installation which was installed to previous regulations will have observations made and codes applied to any safety related non-compliance.

The regulations are changed to improve safety and some of the reasons for carrying out an eicr is to ensure its continued safety for use, highlight improvements which could be made in light of advances in technology and regulations and to help bring older installations up to current standards.

Yes this can seem a little over the top in domestic installations, but domestic installations are only a small part of the broad scope of bs7671.
 

Reply to Was RCD protection required for cables <50mm in 2007? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
530
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
627
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
674
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock