have installed a few 9kW under sink heaters, switch on when hot tap is operated. but would suggest separate units, one for each room. each on it's own dedicated 40A or 50A circuit, with local 45A isolation. 6mmcable may just do depending on length of run and installation method, but you may need to specify 10mm.
bear in mind that overload protection is not required, only fault protection.
 
Many options. If instant water heating is needed, then one 11.5 kW instant water heater can be fitted. 11.5 kW is the maximum on a single phase supply.

Look into instant hot water taps. A Qooker type of tap for the kitchen also giving boiling water, so the kettle can be ditched to liberate worktop space. The 11.5 kW instant water heater can then just do the bathroom with the kitchen hot tap draw-off not influencing the shower. Of course bath fills will not be brilliant. If a shower only, a great way to go, but have an eco aerated shower head.
 
Assuming a 100A supply of course.
[automerge]1591029222[/automerge]
I find that crazy. No overload protection. How many would leave it out?
how can it overload. it's a fixed load. it can go open, in which case it won't work, or it can short (or the cable to it) in which case you have short circuit protection (fault protection).
 
How can you get an overload on a fixed resistive load such as a water heater?
The element cover can break down with the L in contact with water raising the current draw not tripping on fault but overload. I have seen it happen. If there is a spur off a 32A ring via a J-box, only to say an immersion heater element, I believe the regs say no fuse is needed on that spur (fixed restive load), while everything else seems to need one, even a spur to a garden office or garage - not 100% sure on that. To me that is total nonsense. The cost of putting in over-current protection is pennies.
 
The cost of putting in over-current protection is pennies.
There is (almost) always will be over current protection as the regulations require protection of cable against a short.

But overload protection is not always required as some loads should not have the possibility of an overload fault. As you point out, that might be an optimistic assumption in real life!

It is a bit like the requirements for RCD protection, these days the majority of domestic circuits require it (for one reason or another) but not for things like fixed heaters. Which is a shame as that is exactly the sort of thing best suited to picking up a partial heater element fault!
 
The element cover can break down with the L in contact with water raising the current draw not tripping on fault but overload. I have seen it happen.

The cost of putting in over-current protection is pennies.

That is not an overload situation, the load has not been increased over its design limits, that is a fault. Albeit a very rare and unusual fault that will take a long time to clear.

The cost of designing with overcurrent protection in place on a domestic job is usually a matter of pennies or pounds yes, but there is a whole world outside of domestic work where it can be a very different story.
 
For a heater the distinction is probably academic, if you have a load taking X amps then you size your cable for that and fit a MCB at the matching level. So it would be unusual for the OCPD not to also provide overload protection.

Where you see the difference is something like a garage feed (again!) when you might have a planned load of, say, 20A and select a cable to match, then the garage CU has a 20A MCB that provides the overload protection. But the feed for the cable might be a 40A or more fuse that will clear in under 5s on a short but is not offering overload protection for the 20A-rated cable.
 
Where you see the difference is something like a garage feed (again!) when you might have a planned load of, say, 20A and select a cable to match, then the garage CU has a 20A MCB that provides the overload protection. But the feed for the cable might be a 40A or more fuse that will clear in under 5s on a short but is not offering overload protection for the 20A-rated cable.

This would not comply as the load is not fixed in this case.

A better example would be a feed to a motor starter where the overload protection is incorporated in the starter.
 
A better example would be a feed to a motor starter where the overload protection is incorporated in the starter.
In an industrial setup that would be the classic example for sure: the feed OCPD is simply for hard faults and there is another system (i.e. the motor starter) that is engineered to have the appropriate time/current characteristics needed to protect the motor against overload in operation.
 
For a heater the distinction is probably academic, if you have a load taking X amps then you size your cable for that and fit a MCB at the matching level. So it would be unusual for the OCPD not to also provide overload protection.
I have seen a j box in a 32A ring forming a spur, serving only an a 3kW immersion with only a 20A switch between the immersion heater and j box. Well it had a flash neon light on it to make it look better. No over-current protection whatsoever except the 32A mcb at the main CU. A 3kW immersion's current draw is not constant as it depends on the voltage, which may fluctuate during day for various reason.
 

Reply to Water heater in the Central Heating Systems area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock