This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician replace the front part of my service entrance from the weather head to the meter socket. The main panel was updated about 10 years ago and is not in need of replacement.
The grounding paths are currently this:
-Green screw correctly bonding neutral bar to the box.
-#6 bare running continuously (no splices) outside to 2 rods about 7 feet apart.
-#6 bare that runs to the water pipe right as it enters through the basement wall.
-#6 bare short jumper across the water meter.

The electrician estimating the job said that the #6 from the box to the water pipe needs to be replaced because it now has to be a continuous wire through a clamp at the water pipe entrance and then across the meter. He said “a lot changed in the nec2020. Is he correct or does the jumper wire still satisfy? I hate to think he's adding unnecessary work but I don't want to question him unless I can cite my case.
 
This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician replace the front part of my service entrance from the weather head to the meter socket. The main panel was updated about 10 years ago and is not in need of replacement.
The grounding paths are currently this:
-Green screw correctly bonding neutral bar to the box.
-#6 bare running continuously (no splices) outside to 2 rods about 7 feet apart.
-#6 bare that runs to the water pipe right as it enters through the basement wall.
-#6 bare short jumper across the water meter.

The electrician estimating the job said that the #6 from the box to the water pipe needs to be replaced because it now has to be a continuous wire through a clamp at the water pipe entrance and then across the meter. He said “a lot changed in the nec2020. Is he correct or does the jumper wire still satisfy? I hate to think he's adding unnecessary work but I don't want to question him unless I can cite my case.
You can splice at the first or second ground rod but you will need an extra tear drop or acorn for a 5/8 ground rod. You are allowed only on wire per acorn. You have to bond metal piping
 

Reply to Water pipe/ meter ground in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock