we are considering to open a business in the UK and we have a machine with a 60HP hydraulic pump, it is 3 phase.

we are being offered a unit to use and the owner is telling us the supply is 3 phase with 30KVa

our question is will the supply be big enough to run the machine with the pump
 
is the supply 30kVA per phase or total?
 
It sounds like a single phase 80A supply to me.

Could be 3ph but that would be around 45A fuse, which sounds low even for a sub-let industrial unit or similar
 
No, the supply is not big enough. The motor has a full load current of around 85 amps running (60kVA) but depending on the starting method, even a 100A (70kVA) supply might not be adequate. Where one large motor makes up much of the electrical load of an installation, its starting current is usually the main consideration, as the voltage drop during starting can cause other electrical equipment to malfunction.

You will need to liaise with the people on site who provide the supply (assuming it's not direct from the mains) and an electrician with experience in motor supplies.
 
The motor will probably run up to speed under the relatively light load of just pumping oil round in a circle, but, as the last post states, the supply's not big enough for the load, even when the pump's already running.
 
Your best plan is to get some industrial electrician in to look at the setup in detail, it seems it is not enough but equally it is not a very "standard" limit (usually 63/80/100A so 43/55/69kW), so it might be fed from some incoming board in the unit.

Depending on the cost and limits for motor start up it might be worth seeing if you can have a soft-start system added to ramp up the hydraulic pump motor more gently and keep the surge current down. That might be cheaper than a supply with enough headroom!
 
Thank you all for the reply's its pretty much as i suspected myself, i calculated we need around 50KVA for this machine and to be able to keep the lights turned on

The machine has a programable softstart so we could ramp it up slowly which was my initial thinking but signing a 5 year lease with a 50/50 possibility to run this machine could be a mistake.
Once the motor has started the actual running load is quite low, it is basically ticking over to keep the oil flowing to 2 100mm cylinders that are shuttling against each other.
 
If the site is otherwise good for you then speak to the owner about getting an independent electrician in to look at what is possible and cost-effective in terms of supply upgrades.

If they have a beefy supply to the site but it is split on 45A MCB/MCCB/switched-fuse feeds then it might well be affordable to get a bigger supply share, they owner might even provide it as part of a 5 year lease to secure your custom.
 
Last edited:
If the site is otherwise good for you then speak to the owner about getting an independant electricin in to look at what is possible and cost-effective in terms of supply upgrades.

If they have a beefy supply to the site but it is split on 45A MCB/MCCB/switched-fuse feeds then it might well be affordable to get a bigger supply share, they owner might even provide it as part of a 5 year lease to secure your custom.
The site is more or less ok otherwise but I spoke with the owners yesterday and they are telling me a new supply from the sub-station would be the only option, depending if there is the extra available power there, he wasn't able to tell me anything more, apart from everything would be at our expense.
we are trying another couple of options in the area today so hopefully we can get something moving.
 
OK, probably best to look around then. Good luck and let us know how you get on!
Well in the meantime thanks for the great advice and I will post how we get on, I only found this
forum yesterday and I'm already enlightened and I would say it will help me more when needing a good contractor to help with the setup of our equipment. After the isolator I'm more than capable I have 33 years as a electromechanical CNC service engineer but before the isolator I prefer the professionals.
 
Same job as my son in law! He did a 700 mile round trip on Tuesday, and a 400 mile one yesterday. He only left here after normal leave work time, and was home again by just after midnight.
I went to the UK on the 14th Jan got home on 24th at midnight with a 3100Km round trip from my home in Germany, 2 covid tests along the way as well, now in quarantine for 10 days so I feel his pain lol
 

Reply to We are opening a new business in the UK we have Power Question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
577
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
386
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
693
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock