Discuss Electrical PLC Control Panel in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
We have a Electrical PLC Control Panel that has to supply 45 Fused Spur units, do I need to protect these with an RCD, we have a 10A Type D MCB at the moment.
Each Fused spur controls an electronic Volume/Pressure controller which is rated at 130mA.
 
45 seems an awful lot of points for a circuit, no matter what load.
Why the D type?
Regarding RCD, what's the environment and wiring system, for starters?
 
45 seems an awful lot of points for a circuit, no matter what load.
Why the D type?
Regarding RCD, what's the environment and wiring system, for starters?
Its an Industrial system, we control Air Flow into Laboratories and we have Electronic controls, each unit is supplied by 230v AC via a Fused Spur.
But I need to put some sort of MCB into my panel, and need to know purely if it should be via an RCD or just a standard MCB.
Once these are switched on then they wont be switched off except for maintenance.
The Type D is purely for inrush, although they are very low current each (130mA) it could be a type B or C
 
What's the installation method?
 
Whether an RCD is needed will depend on the type of wiring installed. If the unit itself might be fed from an unprotected supply it would be sensible to have the option of an RCD, although in situations where it is not needed, possibly better omitted.

How many circuits would these 45 points be divided amongst? Surely not all 45 on one MCB? How long might the circuit cables be in a typical installation?
 
Whether an RCD is needed will depend on the type of wiring installed. If the unit itself might be fed from an unprotected supply it would be sensible to have the option of an RCD, although in situations where it is not needed, possibly better omitted.
My thoughts exactly. Plus, if all these outlets are powering micro-electronics then I'd be suggesting a 100mA B type RCD - hence, split the circuits down regardless and have them spread over 30mA B's
 
Whether an RCD is needed will depend on the type of wiring installed. If the unit itself might be fed from an unprotected supply it would be sensible to have the option of an RCD, although in situations where it is not needed, possibly better omitted.

How many circuits would these 45 points be divided amongst? Surely not all 45 on one MCB? How long might the circuit cables be in a typical installation?
My thoughts too, basically as questioned in #2 and #6.

The way I would install the system, RCD protection would be a no.....but it's all dependent, as said.

With 45 airflow control points, how many fans are involved, etc?
Is it some sort of monitoring/control for an existing air extract system?
 

Reply to Electrical PLC Control Panel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock