hi

I have come across a problem with a ring main thats been recently installed in a new kitchen, obviously there are 2 earth legs yet whenever the cpc on one side of the ring (outgoing leg for example) is conected to the earth bar in the unit the rcd trips, however when the other leg (incoming leg) is conected then the rcd wont trip and neither will the function button operate the rcd, its like its frooze! these problems are the case if only one leg is conected at a time and if both are conected then the rcd will either trip or freeze depending on which leg is conected first, the freeze leg first and the rcd stays on, trip leg first and it trips! i have done continuity tests on all legs and all readings are what id expect including the cpc at roughly 1.76 times the r1 and rn reading. insulation resistance is also coming back great than 200 mega ohms.

has anyone please got any idea what this could be as i am totally beat by this!!!!

thanks in advance
 
taking 2 obvious possibilities. neutral in wrong bar, or something plugged in, trapped cable , but fooling IR test ( has been known ). ain't got a clue at this stage mate.
 
taking 2 obvious possibilities. neutral in wrong bar, or something plugged in, trapped cable , but fooling IR test ( has been known ). ain't got a clue at this stage mate.

I have to agree with you. Sounds like one of the wires has got mixed up with another inside the distribution board and has ended up on the wrong bar.
 
try disconnecting all the other circuits associated with that rcd, neutrals as well so that you are starting with a clean side to the cu and then reconnect your problem ring main. if it works ok, then your problem can be somewhere else, that can happen sometimes, faults can come from other circuits, dont ask me why or how.
 

Reply to well puzzeled!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
712
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock