S

scintillasam

Hi,

I just done a job today and got some reading of 7ohms, on continuity of a light circuit (B6 CB) this is the highest I have yet seen
is this still ok? Or is this a problem?

Cheers
 
either you've got an extremely long circuit, or bad connections. yes. 7Ω is a priblem
 
about 0.7Ω-- 1/10 of what you say you are getting.
 
if so i nominate him for one of these:



514Z45L6bgL._SL110_.jpg


and when are some guys going to learn the difference between r1 an R1? it's like meerkat and market. different words, different meanings. ssssimplesss
 
Was there a switch in circuit? Poor/dirty contacts can cause high readings. Operating the switch a few times will often produce a better results.
 
Hi,

I just done a job today and got some reading of 7ohms, on continuity of a light circuit (B6 CB) this is the highest I have yet seen
is this still ok? Or is this a problem?

Cheers
theres no fixed value for R1 R2....just a suitably low value....but 7 ohms?...
come on what do you think...
for a start it wont meet a Zs for a 6A MCB to BSEN60898...will it...
 
Move to another point on the lighting circuit and retest then compare the readings.

Loose connection IMHO - are the CPC's twisted together or connected "properly"?
 
Thats why I put theoretically. Done an ecir last year where the tenant had a very damp wall and the zs was 316 ohms! My boss told me to leave it as that was within regs. Don't agree with it myself
 
Thats why I put theoretically. Done an ecir last year where the tenant had a very damp wall and the zs was 316 ohms! My boss told me to leave it as that was within regs. Don't agree with it myself
no...its p!ss poor....
we have the means to get it down to a decent level....so why take the half arsed approach to it all?...
beats me....
 
Thats why I put theoretically. Done an ecir last year where the tenant had a very damp wall and the zs was 316 ohms! My boss told me to leave it as that was within regs. Don't agree with it myself

Thats why the EICR needs a C4 - requires investigation.
 

Reply to What a normal r1 = r2 result should be on a light circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
724
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
383

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock