During the no-load test of a transformer, the primary winding is connected to an AC source without any load connected to the secondary winding. In this condition, the transformer draws only magnetizing current which is required to magnetize the core and establish a magnetic field in the transformer. The unbalance current during the no-load test of a transformer may be caused by several factors including:What are the causes of unbalance current during no load test of transformer?
Thanks for answering, Transformer was in service for approximately 20 years, when the problem arised we performed all the tests, including Insulation resistance, Winding resistance, TTR, Short cicuit test etc. all test results are satisfactory, yet Transformer takes unbalance current on no load.
How big is the imbalance? Have you got the no-load current values? The incoming voltages?
Also when / how did you notice there was a problem?
If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie.
How big is the imbalance? Have you got the no-load current values? The incoming voltages?
Also when / how did you notice there was a problem?
If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie. or @plugsandsparks
TR rating: 5KVA, Step up: 0.470KV / 22KV, No Load current: 8Amp, 0.14Amp, 7.8Amp, Primary side applied Voltage: 0.4KV, Transformer service is as HV power supply unit including rectifier circuit.How big is the imbalance? Have you got the no-load current values? The incoming voltages?
Also when / how did you notice there was a problem?
If it really is recent then it is unlikely to be the core (unless someone applied a LOT of force, or an earthquake) and that would suggest insulation failure as most likely to me. But I don't know as much on this as the likes of @Julie. or @plugsandsparks
What is the winding group?TR rating: 5KVA, Step up: 0.470KV / 22KV, No Load current: 8Amp, 0.14Amp, 7.8Amp, Primary side applied Voltage: 0.4KV, Transformer service is as HV power supply unit including rectifier circuit.
Primay side winding resistance: 629m-Ohm, 643m-Ohm, 631m-Ohm
No, Rectifier is not connected, Primary is delta connected at 400V and Secondary is star connected at 22,800V.I can see why you are querying these numbers. When you say there is a rectifier on the output is this rectifier connected when you are seeing these numbers? - Has the rectifier been tested to ensure all stages are working ?
dY11 and Primary is delta connected at 400V and Secondary is star connected at 22,800V.What is the winding group?
Yny Or Ynd1?
OKdY11 and Primary is delta connected at 400V and Secondary is star connected at 22,800V.
As for now, we do not have access to each phase coil separately.Have you got access to each set of windings separately at some connector board?
I.e. can you separate the delta and energise each of the 3 separately to test each on a single phase supply?
Yes, Secondary winding resistance is: 2.83K-Ohm, 2.82K-Ohm, 2.83K-Ohm
The star point is not earthed, All the transformer test results are satisfactory, Test we conducted are following;OK
Since you see the current between two phases on the delta winding, this means the one winding is either at fault, or (more likely) the secondary has a fault - I would guess one high voltage winding has a fault somewhere along its winding to earth (the star point being earthed) or has an inter-turn winding fault.
This phase will be the one corresponding to the branch of the delta connecting both current taking phases (~8A).
Can you flash test the hv windings - ~27-35kV as it may be an insulation breakdown issue, so won't be shown via an insulation resistance test?
If its an inter-turn winding fault it is a little more difficult to detect with an assembled tx.
(The above assumes there is absolutely nothing connected on the hv side - obviously if there is a single phase load/fault in that part of the system it will reflect as a phase-phase load/fault on the primary )
What voltage did you apply to the primary side?The star point is not earthed, All the transformer test results are satisfactory, Test we conducted are following;
IR (Both Windings), TTR, Open Circuit Test, Winding resistance
400V and no load current was; 7.79A, 0.14A, 8.15AWhat voltage did you apply to the primary side?
Test voltages400V and no load current was; 7.79A, 0.14A, 8.15A