What size cable for 2 extractor fans in a public toilet?
One with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.
Of a type suitable for the conditions where installed.
Technically correct but somewhat unhelpful
Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.
In the nicest way possible, if you need to ask this you shouldn't put yourself in the firing line.
Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?
That wasn't very clear from the question!
So you are saying it's currently 20 amp RCBO with 1.5mm 3 core.
Are there any fused isolators for the fans or are they connected directly?
At the moment my only answer is that no installation method of 3 core flat PVC 1.5mm cable is rated for 20 amps. I was wondering if there were FCU's by the fans and that overload protection was provided that way.
It's likely the RCBO is oversized but can't be sure without knowing more about the fans who knows.
If the OP has a clamp meter it would be interesting to know the current draw with both fans on.
Strictly speaking method C is 19.5 amps. But we won't haggle over 0.5 of an amp. In fact running a 1.5mm directly to the 2 fans is also perfectly safe on a 20amp rcbo. But is it conventional, good practice or advisable? No
Is it not 17.5 amps for a 3 core or am I losing plot again?!
Table 4D2A:
If the rcbo feeds the fans directly than they can be treated like any "End of line" appliance and overload protection omitted. Short circuit protection only required and the 20 amp RCBO covers that
It would be oversized if the 1.5mm was connected to a circuit where the loading can't be controlled directly, like a socket circuit socket
In principle that's not an issue. Both fans won't take more than an amp or 2.Well under the capacity of the cable and the rcbo. The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!
Reply to What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi , I’m going install a commercial 450mm extractor fan , what size and type of cable should i use ?
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Hello, I currently have two switches in my bathroom. One controls the lights above the sink and the other controls a light above the toilet and...
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...