Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb.
I know this is bad practice to install unless using bigger SWA to achieve required csa's in awkward spaces to terminiate.

My question is what code is this? Im going with C3 with recommendation to rectify, but there is an inadvertent danger if 1 leg had a loose termination or worse was removed causing remaining leg to bear the load while being protected by an over rated mcb.

Any help greatly appreciated.

Smarky
Smarky
 
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb.
I know this is bad practice to install unless using bigger SWA to achieve required csa's in awkward spaces to terminiate.

My question is what code is this? Im going with C3 with recommendation to rectify, but there is an inadvertent danger if 1 leg had a loose termination or worse was removed causing remaining leg to bear the load while being protected by an over rated mcb.

Any help greatly appreciated.

Smarky
Smarky

Are both runs exactly the same length and routing?
 
No worries. I was going to type something more in depth but I decided to sit in the garden with a beer. I've coded that C3, because two beers will be an improvement.
Im about to do exactly the same and open a couple myself, Its nice and sunny where I am, enjoy!!!!!
 

Reply to What code for this EICR if any in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
I recently undertook an EICR report for a small house and the conservatory extension had a separate fuseboard which was fed from a 13A plug top...
Replies
62
Views
6K
Hi all Currently carrying out an EICR on a senior school. I constantly find myself questioning my codes as I always go on the side of caution and...
Replies
22
Views
6K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
12K
Hi Im newto this forum and hello to everybody. Im experienced electrician with 15 years of experience in all kind of domestic premised. Some...
Replies
42
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock