I just have a question about the RCCB seen in the picture below.
It is a 63A RCCB protecting the 32A shower circuit, 32A cooker circuit and 2 x 32A socket circuits. My concern is that the rated current of the RCCB is being exceeded. Even with diversity applied it is >63A. I realise we see this often with boards like this, but to start with the RCD test button was not working and also the RCD did not trip with any tests. I then manually switched off the RCD. Following this, the test button worked and the x1 and x5 tests were satisfactory.
I feel the RCCB needs changing for a 80A and I would code it a C2. The reason being is that this is such an important device doing such an important job that I don't think we can just say "well it's highly unlikely in domestic house it will be overloaded" (even though it probably won't be), also if it got stuck open once it may do it again. Small probability of occurring, but a very high impact if it does. This leads to a fairly high score on a risk assessment.
What do you guys think?