10 Kw Shower installation, CU 2 floors down and 4 meters back. Approx 10mm2 cable run of 12 meters. Can I spur from lighting circuit in attic above airing cupboard into separate RCD enclosure fixed in airing cupboard to reduce wiring run or do I run fully to CU and install RCBO (if poss)or fix a separate shower RCD enclosure there?
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
G

Grae79

  • Thread Starter Thread Starter
  • #2
Can I spur from lighting circuit
for a shower? are you kidding? :eek: or do you have one of those houses that have lighting done in 10mm and sockets in 25mm? :rolleyes:
 
S

Spudmiester

  • Thread Starter Thread Starter
  • #3
Is this some sort of P**s Take ?
 
D

drcat

  • Thread Starter Thread Starter
  • #4
Cheers, thought not. Ok, New shower RCD enclosure, Split tails from a Henley block to feed Shower RDC Enclosure.
 
S

Spudmiester

  • Thread Starter Thread Starter
  • #5
Cheers, thought not. Ok, New shower RCD enclosure, Split tails from a Henley block to feed Shower RDC Enclosure.
Actually you need a MCB as well as RCD..........OR you could use an RCBO.
 
S

sparkyork

yeah i think this chap was having a friday evening laugh!! he's worded stuff as a sparky would! sept for the lighting circuit thing obviousyl
 
G

greekislandlover

  • Thread Starter Thread Starter
  • #7
This is what happens when you put a shower through lighting cable fed from the ring. It works once (briefly) and then you get your house rewired :)



1.5mm 6242Y from ring



Chock strip to connect the 6242Y from ring to 6243Y 1.5mm to shower. Got a bit warm eh;)



Where shower used to be.
 
S

Shakey

  • Thread Starter Thread Starter
  • #10
Cheers, thought not. Ok, New shower RCD enclosure, Split tails from a Henley block to feed Shower RDC Enclosure.
remember if you are spliiting those tails about 'single point of isolation':rolleyes:

Oi worms! Get back in that can:p:p:p
 
D

drcat

  • Thread Starter Thread Starter
  • #11
Service Head -> 2 tails -> Meter -> 2 tails -> Isolation switch (Already in place) -> 2 tails (25mm2)-> DP Henley -> four tails (25mm2) -> existing CU & Separate Shower CU (63A 30mA RCD, 50A MCB) and I think 16mm Earth from Shower CU to Existing CU. I'm buying the stuff in, mate supposed to be fitting 'em, he's a spark. I just wanted to know if there was a better / easier way really (and I was trying to show off), hadn't thought properly 'bout the light circuit spur thing, thinner cable and lower rated MCB an all that - I'm a chippie see. If I can't nail it or screw it i'm stumped! I did do 2 yrs of 'leccy apprenticeship 20 yrs ago... shh! - but didn't learn 'owt except for mitring trunking, chasing walls, Lifting / replacing loft insulation and making lots of tea. As it happens, the guy I was apprenticed to got electrocuted and killed on site. I'm not a fan of electric, I don't know how you guys work 'Live'. Bloody stupid if you ask me. Though I'm OK spurring the odd socket here and there but thats about it. When I told sparky mate what I posted, he pi553d himself laughin'

Oh Aye - One more thing - I've been advised that Main Earth Bonding should be upgraded to 10mm as there is more load (I have a 60 amp service head) with this shower but sparky mate reckons it'll be OK as is... Whats the general concensus? Main earth bonding refit would require power cut by DNO yes? Would the DNO be the ones who upgraded the Main Earth Bonding? I have a TN-C-S system so would PEN conductor need upgrading also? Cheers!
 
Last edited by a moderator:
D

drcat

  • Thread Starter Thread Starter
  • #13
stick to the wood butchering
Yes, very constructive - but can you answer the questions? Ta.
 
Last edited by a moderator:
W

wayne

  • Thread Starter Thread Starter
  • #14
sorry didn't realise there was a question worth answering;)
 
S

Shakey

  • Thread Starter Thread Starter
  • #15
Service Head -> 2 tails -> Meter -> 2 tails -> Isolation switch (Already in place) -> 2 tails (25mm2)-> DP Henley -> four tails (25mm2) -> existing CU & Separate Shower CU (63A 30mA RCD, 50A MCB) and I think 16mm Earth from Shower CU to Existing CU. I'm buying the stuff in, mate supposed to be fitting 'em, he's a spark. I just wanted to know if there was a better / easier way really (and I was trying to show off), hadn't thought properly 'bout the light circuit spur thing, thinner cable and lower rated MCB an all that - I'm a chippie see. If I can't nail it or screw it i'm stumped! I did do 2 yrs of 'leccy apprenticeship 20 yrs ago... shh! - but didn't learn 'owt except for mitring trunking, chasing walls, Lifting / replacing loft insulation and making lots of tea. As it happens, the guy I was apprenticed to got electrocuted and killed on site. I'm not a fan of electric, I don't know how you guys work 'Live'. Bloody stupid if you ask me. Though I'm OK spurring the odd socket here and there but thats about it. When I told sparky mate what I posted, he pi553d himself laughin'

Oh Aye - One more thing - I've been advised that Main Earth Bonding should be upgraded to 10mm as there is more load (I have a 60 amp service head) with this shower but sparky mate reckons it'll be OK as is... Whats the general concensus? Main earth bonding refit would require power cut by DNO yes? Would the DNO be the ones who upgraded the Main Earth Bonding? I have a TN-C-S system so would PEN conductor need upgrading also? Cheers!
well to answer the question, you would need to clarify, are you talking about earthing or bonding - there is no such thing as earth bonding;)

are you talikng about the emain earth or the bonding going to your incoming gas/water?
 