hi guys,

what is the MOST likely cause of high resistance when testing continuity of cpc?

I know likely reasons could be loose terminations, bad terminations (e.g not all wiring strands in connection), dirty connectings, ect

But what would you say is the MOST likely reason for the high resistance reading fault?

thanks magpie
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
D

Deleted member 26818

Depends how you are conducting the test.
If using a 3 pin plug lead, then corrosion in socket.
Otherwise, as you say a high resistance joint.
 
S

Silly Sausage

hi guys,

what is the MOST likely cause of a high resistance MEASUREMENT when testing continuity of cpc?
Also, a bad contact with your probes for the above.
Have a good scratch with your probe tips or crocs to make sure you get a good contact.
 
K

Knobhead

Tell us what you think could cause the problem. We'll help then, this isn't a homework site.
 

Richard Burns

-
Mentor
Arms
Esteemed
Most likely would be an insecure termination.
Corrosion, wrong size cables, poor continuity of conduit used as cpc, would all be longer term problems but the loose connection is more prevalent I would say, but Archy's one is good.
 
  • Thread Starter Thread Starter
  • #7
thanks guys,

yeah archy made a good point about the probe tips, but i think its looking more at faults on the installation.

thanks again guys
 
S

sparks1973

always grab both crocs around conductors...hold em firm when in DC low ohms.....best way that...
low batterys in MFTs/seperates will give stupid values sometimes.....as mentioned above high resistance joints...spurs of course and dirt/filth in shutters so wipe the plugtop in and out a bit till it clears and oxidisation/scale on bare CPCs (especially older cable).....
 

Reply to what is the MOST likely cause of high resistance when testing continuity of cpc in the Electrical Forum area at ElectriciansForums.net

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Select the ways in which you gain online business

  • MyBuilder.com

  • Federation of Master Builders

  • CheckaTrade.com

  • RatedPeople.com

  • TrustaTrader.com

  • Which? (TrustedTraders.Which.co.uk)

  • MyJobQuote.co.uk

  • Yell.com

  • Google Paid Advertising

  • Own Website with Natural Ranking (SEO'd website)

  • Social Media (Facebook Twitter Instagram etc)

  • Word of Mouth Only for me


Results are only viewable after voting.

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Top Bottom