hi guys,

what is the MOST likely cause of high resistance when testing continuity of cpc?

I know likely reasons could be loose terminations, bad terminations (e.g not all wiring strands in connection), dirty connectings, ect

But what would you say is the MOST likely reason for the high resistance reading fault?

thanks magpie
 
D

Deleted member 26818

Depends how you are conducting the test.
If using a 3 pin plug lead, then corrosion in socket.
Otherwise, as you say a high resistance joint.
 

Archy Styrigg

Mentor
Electrician's Arms
Trainee Access
Messages
10,143
Location
Manchester
hi guys,

what is the MOST likely cause of a high resistance MEASUREMENT when testing continuity of cpc?
Also, a bad contact with your probes for the above.
Have a good scratch with your probe tips or crocs to make sure you get a good contact.
 
K

Knobhead

Tell us what you think could cause the problem. We'll help then, this isn't a homework site.
 

Richard Burns

Respected Member
Mentor
Electrician's Arms
Trainee Access
Messages
9,926
Location
Cambridgeshire
Most likely would be an insecure termination.
Corrosion, wrong size cables, poor continuity of conduit used as cpc, would all be longer term problems but the loose connection is more prevalent I would say, but Archy's one is good.
 
OP
P

paulthemagpie

Regular EF Member
Messages
260
Location
North
thanks guys,

yeah archy made a good point about the probe tips, but i think its looking more at faults on the installation.

thanks again guys
 

sparks1973

Regular EF Member
Messages
1,027
Location
Leeds
always grab both crocs around conductors...hold em firm when in DC low ohms.....best way that...
low batterys in MFTs/seperates will give stupid values sometimes.....as mentioned above high resistance joints...spurs of course and dirt/filth in shutters so wipe the plugtop in and out a bit till it clears and oxidisation/scale on bare CPCs (especially older cable).....
 