hi guys,

what is the MOST likely cause of high resistance when testing continuity of cpc?

I know likely reasons could be loose terminations, bad terminations (e.g not all wiring strands in connection), dirty connectings, ect

But what would you say is the MOST likely reason for the high resistance reading fault?

thanks magpie
 
Most likely would be an insecure termination.
Corrosion, wrong size cables, poor continuity of conduit used as cpc, would all be longer term problems but the loose connection is more prevalent I would say, but Archy's one is good.
 
always grab both crocs around conductors...hold em firm when in DC low ohms.....best way that...
low batterys in MFTs/seperates will give stupid values sometimes.....as mentioned above high resistance joints...spurs of course and dirt/filth in shutters so wipe the plugtop in and out a bit till it clears and oxidisation/scale on bare CPCs (especially older cable).....
 

Reply to what is the MOST likely cause of high resistance when testing continuity of cpc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
970
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock