So why wouldn't a 13amp fuse blow before a 32amp circuit breaker?
Just look at the current/time plots for them.

Typically with a fuse and larger MCB you will find generally:
  1. The fuse blows first (up for PFC up to the MCB magnetic trip point)
  2. Then you find the MCB trips first, and the fuse survives (if MCB I2t let-through is below the per-arcing I2t of the fuse)
  3. At very high PFC you find the MCB trips but the fuse has also blown (as the blows in under the time for the MCB to operate, typically 5-10ms).
 
Rational Argument:
Domestic general purpose socket outlet circuits;
2.5mm ring final circuit, protected by 25amp BS EN 60898 mcb, supplying BS 1363 plastic socket outlets.
Light industrial general purpose socket outlet circuit;
4.0mm ring final circuit, protected by 32amp BS EN 60898 mcb, supplying BS 1363 'metalclad' socket outlets.

History:
Domestic general purpose socket outlet circuits;
2.5mm ring main, protected by 30amp fuse carrier with 20amp fuse wire/cartridge, plastic socket outlets.
Light industrial general purpose socket outlet circuits;
4.0mm ring main, protected by 30amp fuse carrier with 30amp fuse wire/cartridge, 'metalclad' socket outlets.
 
Last edited:
Rational Argument:
Domestic general purpose socket outlet circuits;
2.5mm ring final circuit, protected by 25amp BS EN 60898 mcb, supplying BS 1363 plastic socket outlets.
Light industrial general purpose socket outlet circuit;
4.0mm ring final circuit, protected by 32amp BS EN 60898 mcb, supplying BS 1363 'metalclad' socket outlets.
The argument being?
 
The important working parts of a metalclad socket-outlet (near the points at which heat is generated) are usually made of the same plastics as an all-plastic one, although an enclosure with more of its surface made of metal might provide better containment of burning material from within. Within a BS1363 plug and socket-outlet pair, heat is generated mainly at points of high current density, such as (in approximately decreasing order of significance)
  • Fuse element
  • Fuse clips
  • Socket contacts
  • Switch
  • Plug terminals
  • Socket terminals
Thus two of the principal sources of resistive heating are outside the containment offered by a metal socket faceplate anyway. The quality of manufacture, installation and any deterioration of the contact surfaces are key factors in the resistance at various points and the heat generated. So too is the effect of heat on the long-term stability of resistance, which is markedly poor in low-quality accessories.

Or have I missed the point? This whole thread seems to be an exercise in trolling by someone with knowledge of electrical principles, or an attempt to cheese everyone off by someone without, by repeatedly making false statements. I can't tell.
 
If you look on the home page the envelope in the top right corner should indicate a message. Reply to this message.
 
Don't think the OP will be back if you catch my drift :)

Thanks everyone for resisting the urge to say what you really felt.

It's a strange carry on. I dare say he'll be back with some more bizarre postings in a few months.
 

Reply to What is "unwanted tripping"? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Wallbox Fuse Box Lite Single Phase has anyone used one of these? I've installed one feeding a Pulsar Max, the Pulsar Max is set to 32Amp max. The...
Replies
0
Views
189
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
542
This for an apprentice 32 amp mcb /63amp RCD 1) no power to the sockets 2) installation resistance all good. 3) contunuty good. 4) no loses...
Replies
13
Views
626
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock