Hi need advise on cable 25 meters run underground for additional consumer unit in garden outbuilding to acomodate 9Kw sauna heater 10kw water heater 3double sockets 6 down lights and 4 outside lights?Thanks in advance .
 
25mm. that should do. a separate supply might be a good idea.
 
yeah, well from you posted, you need 100A supply. don't think the average house supply can take that much extra load, unless they got 3 phase.
 
yup agree with 25mm2, however without getting the BGB out now haha, come on it is Christmas eve, I suspect a16mm2 may will do the job, well maybe, but 25mm2 sounds right and what I would put in.
 
agree with biff, although 25mm2 is right, well probably right it is best to consider the capacity, too many beers and a thick head is clouding the judgement at the moment haha
 
And how to consider the capacity ?what i can do is only wire cables but not connecting them .I was suggested Henley on main incoming 100amp then 25mm armoured cable. But know Consider capacity??
 
A few questions for you....
Find out if the water heater will be used simultaneously with the sauna??
I'm taking it that this would be an electric shower type load??
What sort of loads are going to be supplied by the socket outlets??
What sort of outside light fittings, eg, not halogen 500W floods i hope...lol!! ??
What earthing arrangement do you have??
 
And how to consider the capacity ?what i can do is only wire cables but not connecting them .I was suggested Henley on main incoming 100amp then 25mm armoured cable. But know Consider capacity??

You wire this supply then you are responsible for the design included expected demand on existing etc etc .... if the main cutout was to operate because you hadn't taken into account the load demand then you could be liable for all costs relating to the rectification and DNO callout.
P.s. just because the cutout carrier may state 100amps dosn't mean the fuse within is that rating so at some point here you will need to liase with the DNO to so the allowance you have to start with.
 
Yet another chancer with not a clue what he's doing.
Look is not your business chancer or not I'm asking because half electricians I called to give me quate came with lots of bul...et you need that and you need that because law states this is how should be and at the end they want 1000 for two days work it's ripp off because I know basics
 
Look is not your business chancer or not I'm asking because half electricians I called to give me quate came with lots of bul...et you need that and you need that because law states this is how should be and at the end they want 1000 for two days work it's ripp off because I know basics

If you know it, just run it all yourself and connect it up and then you may just find out what the 1000ish quid was for. Have you priced up the cable?

I've just installed some 16mm SWA to my own garage and let me tell you, to do it properly it is not cheap.
 
well, don. you should have given more info in your 1st post. it sounded as though you were a sparks that wanted his design work doing for him. what cable size did these sparks quote for?
 
Never had customer say 'that's cheap' after giving them a quote.
They want it done for nothing, hear's a perfect example.
Wouldn't be surprised if the OP attempts a DIY solution.
 
Armoured cable will be over £200 of that £1000, plus all the other bits. All the other qualified electricians are telling you how it should be, yet you who only know the 'basics' think that you are right and they are wrong? You can afford a sauna, outside luxury living space, but want to cut corners getting it powered up?

How much do you pay for a service on your luxury car>

Joker
 

Reply to What size armoured cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
550
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
644
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock