Called to a property which has just been sold to do an EICR
The sockets down stairs including the kitchen were on a 16a 2.5 radial the issue being the Zs for the first couple of sockets were about average readings but the last few and the sockets in the kitchen went from 0.90 ohms to 1.19 ohms. Personally I wouldn’t put a kitchen on a radial but that’s just my preference. But why the higher than normal results could it be a case of more than one spur from a socket That’s giving me high readings also 16a is just not cutting it. The property had an EICR done a few months ago but no concern over higher readings on socket radial for the down stairs sockets including the kitchen being on a 16a 2.5 cable your comments would be appreciated
 
Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below

davesparks

-
Mentor
Arms
Esteemed
The Zs readings will naturally increase the further from the CU you get, 1.19 doesn't sound like a problem on a 16A MCB off the top of my head.
 

gazdkw82

-
Trainee
It's a radial, the further away from the protective device the higher the reading will be. However a sudden jump (like you have here) is a sign of loose termination/bad connection/large distance between 2 points etc.

It's still compliant but worth investigating if it's close to the last (lower reading) point.
 
Is the cpc 1mm or 1.5 - maybe a mix of both plus older wiring plus changes - otherwise connection loose or a hidden connection box.
 

telectrix

-
Mentor
Arms
Esteemed
2.30, before corrections for temp. and Cmin. ( Cmin correction then gives 2.185.
 
  • Thread Starter Thread Starter
  • #12
What about the kitchen ,it is running of f it as well 16a would this be enough or should I suggest putting a separate feed in.
 

Electric Magic

-
Arms
Esteemed
What about the kitchen ,it is running of f it as well 16a would this be enough or should I suggest putting a separate feed in.
Depends on the load, in most cases one 16A radial is unlikely to provide enough power for a kitchen. Also, 1.19ohms, if there are no poor connections and assuming you are talking about 2.5mm2 twin and earth means the circuit is about 60m long at that point (off the top of my head might be a couple of meters out) and volt drop may well be over 5%

EDIT just noticed you said Zs not R1R2 so my calc and point about volt drop may not be valid, what's the Ze?
 
  • Thread Starter Thread Starter
  • #14
0.20 the thing is I’m not comfortable with the fact downstairs sockets and the kitchen are all on a 16a what do you think.
 

telectrix

-
Mentor
Arms
Esteemed
cut kitchen out of existing radial. leave that for the downstairs sockets, then new 4mm radial or 2.5mm rfc for kitchen. if rfc, you can probably re-use a lot of the existing kitchen wiring.just make it into a rfc.
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to What’s going on with this radial in the Electrical Forum area at ElectriciansForums.net

Test Meter - Forum Sponsors since 2007!
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom