No neutral from bottom of second DP switch to neutral bar. I'm guessing an RCD has been replaced at some point due to nuisance tripping?
 
old split load board with trippy rcd , so some clever sparks swapped out the rcd for a main switch , seen this loads of times
 
my guess is that they re-used the old splt board when rewiring and it tripped out so they took the easy option
 
Having a main switch instead of the RCD is not immediately dangerous or potentially dangerous.

there are issue that can be coded due to inadequate additional protection, but I can’t see the main switch being a Code in itself. What do you think?
 
Having a main switch instead of the RCD is not immediately dangerous or potentially dangerous.

there are issue that can be coded due to inadequate additional protection, but I can’t see the main switch being a Code in itself. What do you think?
Dunno never seen switch with no neutral so Dunno how to code this also rcd sometimes tripping on zs low 3lead test is neutral arrangements can cause that or earthing problem I put as earthing problem
 
Dunno never seen switch with no neutral so Dunno how to code this also rcd sometimes tripping on zs low 3lead test is neutral arrangements can cause that or earthing problem I put as earthing problem
Just ask yourself is this issue immediately dangerous? Is someone in imminent danger?
or is there a potential danger? Could some one come to harm if some one does something?

ask yourself if the double pole isolator without a neutral is dangerous and how is it dangerous? Justify your coding.

I don’t like it, I think it’s wrong. just because I don’t like it and think it’s wrong doesn’t mean I can code it. I can’t just say it’s wrong. you have to give a valid reason why it is electrically wrong.

so what do you think? Does it need coding? And why?
 
Dunno never seen switch with no neutral so Dunno how to code this also rcd sometimes tripping on zs low 3lead test is neutral arrangements can cause that or earthing problem I put as earthing problem

What was the earthing problem?
 
Just ask yourself is this issue immediately dangerous? Is someone in imminent danger?
or is there a potential danger? Could some one come to harm if some one does something?

ask yourself if the double pole isolator without a neutral is dangerous and how is it dangerous? Justify your coding.

I don’t like it, I think it’s wrong. just because I don’t like it and think it’s wrong doesn’t mean I can code it. I can’t just say it’s wrong. you have to give a valid reason why it is electrically wrong.

so what do you think? Does it need coding? And why?
Q
 

Reply to Whats wrong with this pic in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock