- Reaction score
- 2
When connected to the fan voltage at connectors is 20v when disconnect from fan voltage is 220v. This down to the capacitor?
Discuss When connected to the fan voltage at connectors is 20v when disconnect from fan voltage is 220v. This down to the capacitor? in the Electrical Forum area at ElectriciansForums.net
I did think this however, i used my fluke mft and my normal martindale voltage tester, with proving unit. It was certainly live.It's most likely that you are measuring a ghost voltage an dthere is in fact no voltage there at all, what tester are you using?
So i was called to a fan not working, it was an inline fan. I could easily access it so I just tested if there was voltage. In the exsiting connections i tested it and it read 20v AC. I thought it was strange thought the 20v might be off the capacitor (its an old fan) so i disconnected the feed and retested it, expecting 0v but actually had 220v AC. Ive recommended changing the fan in question but wonder if its something elseI'm struggling to make sense of that - could you re word it a bit.
L-N
L-E
N-E
No sorry should of been clearYou had 220V between neutral and earth?
But us immediately rectified once disconnection from the device?How would you get 20VAC from a capacitor?
Why did you recommend changing the fan? Nothing you've told us suggests that the fan is faulty as far as I can see.
A voltage which is present when there is no load but disappears as soon as a load is applied suggests that you have a problem with the supply, not the load.
I would suspect a loose connection somewhere in the supply circuit.
Nice one, il take the fan but check all connections as they are accessible. ThanksNo it isn't rectified once the load is disconnected, you are just reading the open circuit voltage with the load disconnected.
With the fan connected you have a series circuit of the what I suspect is a high resistance connection and the load. So if the open circuit voltage is 220V and the closed circuit voltage across the fan is 20V then voltage across the high reisistance connection is 200V.
Thanks will doWhy not start with a few tests to check whether my theory is correct or not rather than randomly checking connections?
I'd like to see a squirrel with 200v across his paws ?either that or a squirrel in the attic.
that'd make his fleas jump.I'd like to see a squirrel with 200v across his paws ?
More likely to toast his nutsthat'd make his fleas jump.
Reply to When connected to the fan voltage at connectors is 20v when disconnect from fan voltage is 220v. This down to the capacitor? in the Electrical Forum area at ElectriciansForums.net
