Thanks for the interest in my earlier question.

I have just paid my DNO a lot of money to install a 3-phase connection with a maximum load of 25kVA.

Is my physics wrong when it tells me that when they fitted 80 amp fuses at the incomer I have 25kVA? I think it's wrong to multiply 230(v) x 80 x 3, but is it correct to multiply 415v x 80 which = 33.2kVA? And if 100 amp fuses were installed do I have 41.5kVA?

Back to shool I think.
 

ElectroChem

-
Esteemed
Arms
Reaction score
346
Just because the DNO has fitted fuses that can handle more than 25KVA, don't just load up and go. You may end up with a sternly worded bill including a charge for exceeding your allowance.
 

Lucien Nunes

-
Mentor
Esteemed
Arms
Reaction score
9,964
I think it's wrong to multiply 230(v) x 80 x 3,

No, it's correct. When dealing with 3-phase supplies that may or may not have a neutral, it's customary to always calculate from the line-line voltage (normally 400V) in which case P = I * 400 * sqrt(3) as this is always applicable. But the power available is the same whether it is drawn by loads wired between the lines at 400V, or from line to neutral at 230V, hence P = I * 230 * 3.
 

DefyG

-
Esteemed
Arms
Reaction score
652
I have just paid my DNO a lot of money to install a 3-phase connection with a maximum load of 25kVA.
Working backwards, if you had a 3ph load of 25kVA pf 0.8, 400v, line current of say 45A would you use a 80A for the circuit fuse?

Maybe the DNO have made a simple typing error and should read 55kVA and not 25?
 

ElectroChem

-
Esteemed
Arms
Reaction score
346
Working backwards, if you had a 3ph load of 25kVA pf 0.8, 400v, line current of say 45A would you use a 80A for the circuit fuse?

Maybe the DNO have made a simple typing error and should read 55kVA and not 25?

I suspect that a single cable size and 80A fuses are just the standard install package the DNO puts everywhere. As long as the cable is properly protected, then perhaps you can pull more load than you officially should, depending on how granular the feedback from the meter is.
 
OP
A
Reaction score
0
I suspect that a single cable size and 80A fuses are just the standard install package the DNO puts everywhere. As long as the cable is properly protected, then perhaps you can pull more load than you officially should, depending on how granular the feedback from the meter is.

OP here again.

Thanks for all the replies - I've now had a long chat with a very helpful chap at my DNO - you might be interested in what was said.

First, whilst I originally applied for 60kVA, that number was a shot in the dark as I had no idea what the cost would be so I thought of a number and doubled it (sort of). As it happens, for any application over 25kVA there's a hefty charge for the quotation itself so I changed the application to the lower number for which there is no charge for a quotation . I only wanted to add a heat pump and EV charge point to a domestic property -it wasn't for a Bit-Mining computer room or whatever.

So, as Electrochem said, the DNO has standard waveform underground cables which they use for "normal" jobs. I actually have another two 3 phase supplies feeding different buildings (so three in total) and have sole use of an 11KV transformer feeding a 100m long, 50mm o/d, aluminium three core cable. That splits into 32mm o/d cables going into the separate buildings. The now standard fitment (just about everywhere, I'm told) 80 amp Lawson fuses are at the end of every cable - even if the rating on the outside of the carrier says 100A - that's the rating of the fuse carrier, apparantly.

So, though I'd applied and paid for 25kVA (about 31kw using the 0.8 correction for real v apparent power) on my most recent connection I could potentially draw much more than that - a total of around 165kVA - over all three supplies.

The transformer, pictured below, shows a rating of 66.7 amps at 433v. With the numbers you've all quoted above I was concerned about unwittingly overloading my part of 'the grid' - hence the phone call to the DNO.

Whatever the potential overload actually is, the DNO works on several assumptions. First that not all potential loads are in use at anything like their maximum 80A per phase at the same time. Second, if they were, that the slow-blow 80A fuses and/or those at the transformer, would not blow at anything like their rating - it could be many (many, many) minutes at a much larger current before they would - I was told. And the transformer can handle much more than its rated maximum - even for some hours.

The moral? Rules (numbers in this case) are for fools and the guidance of wise men? I'm not sure whether I'm overly happy with that but, in my situation, if it all works in practice then so be it.

To widen the conversation, in talking to the DNO people installing my 3-phase supply, I think we have a time-bomb waiting to go off in our local electricity infrastructure. In 40 months time no new houses can have gas or oil heating - so, presumably, heat pumps for them plus all the other homes where people want to switch to electric heating. And in less than 9 years you won't be able to buy a diesel or petrol car - only hybrid or all-electric. And only all-electric cars in 14 years time. How many homes, streets, estates, towns have the supply capacity to accommodate this demand? None around me.


You don't have permission to view attachments. Attachments are hidden.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

Darkwood

Mentor
Esteemed
Arms
Reaction score
10,044
You worry in 40months time no new houses will have gas, you must also realise there will be a drive for them to have alternative sources like solar, they will have significantly better energy efficiency compared to the existing old stock housing out there and may even have some form or air source or ground source heating, recently done a few myself and surprisingly efficient even with snow piled up outside.

I also believe people will learn to put on a jumper instead of having their thermostat on full whack most of the year.
 
OP
A
Reaction score
0
You worry in 40months time no new houses will have gas, you must also realise there will be a drive for them to have alternative sources like solar, they will have significantly better energy efficiency compared to the existing old stock housing out there and may even have some form or air source or ground source heating, recently done a few myself and surprisingly efficient even with snow piled up outside.

I also believe people will learn to put on a jumper instead of having their thermostat on full whack most of the year.
I agree entirely. The problem is that, for homes, wind power isn't a viable solution that compares with solar and, for new solar generation, the domestic market supply chain has largely collapsed because of the removal of the FIT susbsidy.

A Building Reg's requirement could be used to ensure new-builds, probably on an individual but also an 'estate' basis, included a certain amount of on-site generation. Schools built in the 2000's under the BSF (Building Schools for the Future) had generous incentives to install combined heating and electric power generating systems (CHP) using renewable fuels. And thousands of schools took advantage of their large roof areas to install solar panels.

But your last point is especially important - my children's headteacher had a Wooli-Pulli policy which basically meant that kids - and staff - couldn't wear just thin T-shirts or vest tops and then complain of being cold. A long time ago didn't Margaret Thatcher introduce a maximum office temperature of 18c that practically no-one observed?
 

Reply to When is 3x80 amps 25kVA? in the Commercial Electrical Advice area at ElectriciansForums.net

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

Search Forum

Top