Hi, i am having a new kitchen and need to get the water bonded.

i have looked at the pipe work, and it is as follows.

comes from the street straight into kitchen where there is a T piece, 1 side goes out to the garage to feed a tap and the other side goes to a stop cock to control the water for the house.
the tap in the garage is straight off the mains and cannot be turned off with the stop cock.

Can it be bonded from the tap pipe in the garage ?

Cheers
 
you should bond within 600mm of where the water enters the building, before any branch. usually this is after the stop tap, but as you describe it, the garage is tee'd off before the tap. either way, if there is continuity through the stop tap, both the house water and the garage water will be equipotentially bonded, so it doesn't make a lot of difference. personally i would fix the bond on the house side of the tap, ensuring it's accessible for inspection. as you will be introducing an earth potential into the garage, there may be other issues to address.
 
As tele' says, bond just before T piece in the house.
If there are electrics in the garage, then supplementary bond the tap, or ensure all circuits are RCD protected.
Essentially treat the garge as a bathroom.
 
I think tele said to bond on the house side of the tap,
I would agree with that, then if anything is changed before the stop tap it isnt a problem, it doesnt become your pipe until after the stoptap. AFAIAA.
 

Reply to Where to bond water ? in the Australia area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
I have two supplies into a new horstman e7 box, 1 from the offpeak water heating one from standard tariff boost do both suppies go to 1 and 2, 4...
Replies
3
Views
559
Is there still a requirement to bond the main water if everything after the stop cock is plastic? Cheers
Replies
9
Views
4K
I have a 4.8kw solar diverter with 2 x 4.8kw hot water systems. Is there a switch that will only heat one hot water system at a time and switch...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock