Been to a domestic installation today and found that the water and gas are not bonded. The water appears straightforward, however the gas is not so.

The gas service currently enters the house under the floor. A heating engineer has previously teed off here and taken a supply back outside the house and up into the loft to a new boiler installation.

Where would you guys bond to? I'm not keen to bond under the floor - access issues for inspection etc, although this then means that I'm bonding after branched pipework. I could bond outside, near the ground, and run the bonding up the outside wall and across the loft towards the MET on the other side of the house. This may lead to mechanical damage or corrosion issues. Or I could simply bond in the loft where the gas pipe enters.

Any thoughts?
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
S

Spudnik

  • Thread Starter Thread Starter
  • #2
Can you not bond in the meter cabinet?
 
C

Chops

  • Thread Starter Thread Starter
  • #3
The meter cabinet is about 50 metres away at the front of the property (old farm). The gas supply pipe runs underground to the house and pops up at the base of an outside wall.
 
J

jackaria09

  • Thread Starter Thread Starter
  • #4
where did you work? mabey you could bond it where the gas pipe enters in the loft.
 
K

kung

  • Thread Starter Thread Starter
  • #5
Easiest place and nearest point you can get to that enters the house.
 
C

Chops

  • Thread Starter Thread Starter
  • #6
Hi Kung

That would be the loft. But is that the best way of satisfying the regs?
 
K

kung

  • Thread Starter Thread Starter
  • #7
Hi Chops
If this is the nearest point that enters the house you can get to thats fine as long as its bonded.
 
Hi Chops the gas pipe should be bonded within 600m of it entering the property and before any branching off.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #9
Agree with these chaps.

As long as its bonded within 600mm etc it doesn't matter where it is.

The certs now have a 'location if not obvious' box now, so just fill that in with the details.
 
C

Chops

  • Thread Starter Thread Starter
  • #10
Thanks guys

If I go within 600mm and before branched pipework, then its under the floorboards (and carpet / furniture) and then a note on the paperwork and at the CU detailing the location.

Chops
 
S

Spudnik

  • Thread Starter Thread Starter
  • #11
Chops,

If you can avoid putting it under the floor then i think that would be better, regardless of noting it on the cert.

Just MHO.:)
 
C

Chops

  • Thread Starter Thread Starter
  • #12
Well thats the contradiction. I cant satisfy all aspects of the regs here. I cant bond within 600mm of point of entry and before branched pipework and at an accessible point.

It has to be two out of the three. Which aspect do I not satisfy?

Chops
 
S

Spudnik

  • Thread Starter Thread Starter
  • #13
I think that as you are familiar with the installation and if under the floor is the only 'satisfying' option, then bond there, again, noting on the cert and as long as it is accessible for future inspections.
 
G

Guest123

  • Thread Starter Thread Starter
  • #14
Hey.

Might be worth a call to your scheme provider as I know the NIC wouldn't accept a main bonding connection under the floor - maintenance and testing reasons.

Cheers
 
S

Spudnik

  • Thread Starter Thread Starter
  • #15
Hey.

Might be worth a call to your scheme provider as I know the NIC wouldn't accept a main bonding connection under the floor - maintenance and testing reasons.

Cheers
Thats why im not registered with them..:D
 
P

pushrod

  • Thread Starter Thread Starter
  • #16
Well thats the contradiction. I cant satisfy all aspects of the regs here. I cant bond within 600mm of point of entry and before branched pipework and at an accessible point.

It has to be two out of the three. Which aspect do I not satisfy?

Chops
but the regs aren't statutory they are guidelines so if you can justify your choice and you have done what is reasonably practicable i don't really see a problem ( tin hat on) . So to my mind it's up to you and your decision is right.
 
C

claire_r

  • Thread Starter Thread Starter
  • #17
location if not obvious?? does that mean anywhere on the pipework as long as it's labelled on the db? where is that in the regs just out of interest? :D
 
M

maddfridge

  • Thread Starter Thread Starter
  • #18
Been to a domestic installation today and found that the water and gas are not bonded. The water appears straightforward, however the gas is not so.

The gas service currently enters the house under the floor. A heating engineer has previously teed off here and taken a supply back outside the house and up into the loft to a new boiler installation.

Where would you guys bond to? I'm not keen to bond under the floor - access issues for inspection etc, although this then means that I'm bonding after branched pipework. I could bond outside, near the ground, and run the bonding up the outside wall and across the loft towards the MET on the other side of the house. This may lead to mechanical damage or corrosion issues. Or I could simply bond in the loft where the gas pipe enters.

Any thoughts?
hi there

i would suggest you find the gas meter and bond within 600mm before the first branch.

in the cabinet if poss then run to main met

you should not bond under the floor as it is a requirement under the gas regs for access and verification i think this is correct

anybody feel free to please correct me if i am wrong

if you cannot then it is at the first entry point to the building based this assumption from the advice given in the domestic corgi book
 
P

pushrod

  • Thread Starter Thread Starter
  • #19
hi there

i would suggest you find the gas meter and bond within 600mm before the first branch.

in the cabinet if poss then run to main met

you should not bond under the floor as it is a requirement under the gas regs for access and verification i think this is correct

anybody feel free to please correct me if i am wrong

if you cannot then it is at the first entry point to the building based this assumption from the advice given in the domestic corgi book
chops has already said gas meter is 50metres in front of property and first bend is under flloor.
 
C

Chops

  • Thread Starter Thread Starter
  • #20
Thanks for everones input. I'll forget about under the floor. I will bond where the pipework re-emerges outside the property and then loop into another bond clamp in the loft for belt and braces in case of mechanical damage issues to the outside clamp in the future.