Hi all i just want to check if everything is ok with my 1st 50kw solar install.

I have run a submains from an existing main consumer unit which is supplied with a 300mm swa cable so no problems there with volt drop.
The sub board i put in is supplied with 16mm swa on a 50a mcb 10 meters away
I took the 16mm swa firstly through the 3 phase generation meter in a clear enclosure then to the sub board obviously using the same size 16mm tails to the incoming main switch on my subboard.I ran three circuits each on 32a tp mcbs supplying 3 seperate ac 4 pole isolators and 3 sma 15000 tl-10 inverters.Each inverter has 3 strings so 9 dc isolators used.All seems fine.give me your thoughts.
 
Hi all i just want to check if everything is ok with my 1st 50kw solar install.

I have run a submains from an existing main consumer unit which is supplied with a 300mm swa cable so no problems there with volt drop.
The sub board i put in is supplied with 16mm swa on a 50a mcb 10 meters away
I took the 16mm swa firstly through the 3 phase generation meter in a clear enclosure then to the sub board obviously using the same size 16mm tails to the incoming main switch on my subboard.I ran three circuits each on 32a tp mcbs supplying 3 seperate ac 4 pole isolators and 3 sma 15000 tl-10 inverters.Each inverter has 3 strings so 9 dc isolators used.All seems fine.give me your thoughts.

63A mcb would be better at sub board and err where have you put your G59 relays?
 

Reply to Where to wire in 3 phase gen meter? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
511
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
814
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
636
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock