Discuss Whirlpool in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Can anyone help me please?
I'm looking to install a whirlpool bath pump in a domestic bathroom.
The instructions say I have to wire the system independently, but I was hoping to spur off the domestic socket circuit in an adjoining bedroom too a fused switch outside the bathroom. Is this OK? The consumer unit is at the other side of the house!
I've searched these threads, and the only reference I can see condoning using a separate supply refers to the possibility that the motor might cause nuisance tripping? In that case should I use a second RCCB in-line with the fused switch?
I'd be obliged for any clarification.
In another life, Murdoch. I got my sjib grade card back in '79 but gave up the tools about 12 years back when my life took another direction. I'm currently in the process of registering for BS7671 and ECS H&S Assessment.
In re-reading the instructions it says " ... must be wired independently. Do not use the same power supply as other appliances" Which I read as, don't loop the supply from a towel-rail, heater, shower, etc.
I fully intend complying with the manufacturers instructions, i'm just not sure if i'm interpreting them correctly and wondered if someone could help me clarify.
instructions a bit ambiguous. i suppose if you wire a FCU off the RFC, that's independent. that's how i would do it. 3A FCU .
oops, a bit over my 3A. the only problem you'll have with a RCD FCU is no discrimination with the existing RCD in the CU ( assuming that the RFC is on RCD)
As Tele says, but would suggest a 10A fuse in the FCU. I'm guessing you've checked the bonding?? and this is notifiable too!
use a double pole FCU, then it can be isolated. should not cause nuisance tripping unless faulty. might have some leakage ( of water) if a plumber has fitted the thing.
To be honest, I only got a quick sneak peak this afternoon. The original bath has been taken away and the new whirlpool bath is in situ but not fixed down or plumbed in yet. In my days we ran a separate 6mm earth to the bathroom and kitchen, so I'm assuming that is there and I just didn't notice it. The house itself is only about 10 years old.
He's not talking about that bonding, he's on about the equipotential bonding of the gas/water supplies.
If the CU has a 30ma RCD and the gas/water supplies are bonded back to the CU in 10mm cable (if it's a TNCS suply) then all you need do is add an FCU to the nearest ring outside of the bathroom and fuse it down to whatever your load works out to.........simples!
If there isn't an RCD in the CU then you can add a combined RCD/FCU as you already suggested instead of the standard FCU. You still need to check the bonding though.
Reply to Whirlpool in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
1. Does every powered item in bathroom needs fused spur outside? 2. Can separate RCD be required even if the supplied power is under CU RCD (for...
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...