Discuss Why Are Incoming Live/Neutral 16mm and Tails From Consumer Unit 25mm in the UK Electrical Forum area at ElectriciansForums.net

I feel like a rebel now for using 10mm tails out a Henley block to supply an RCBO in a small enclosure before a 4m cable run to an EV charger. All in the meter cabinet. I do like working with 16mm Flexi tails but few suppliers stock them around here
 
Older installations had 16mm tails fitted because that all they need.
In recent years it has become the norm for people working in the domestic sector to fit 25mm tails regardless of what size is actually required.
This has been fuelled by the IETs picture book which shows diagrams of typical supply and CU setups where 25mm tails are fitted.
So now we have a lot of installations with shiny new CUs and 25mm tails, fed via 16mm tails from the cutout which in turn is fed via a 100 year old paper insulated lead sheathed cables of an imperial size a bit smaller than 16mm.

Why electricians these days seem to forget/ignore the theory, science and regulations and choose to follow the herd like a bunch of sheep I don't know.
Not quite sure on what you base some of your facts and why you choose to make the final comment you do
The tail size is more likely carried over from the Electricity Boards, in the board areas I worked MANWEB and NORWEB both specified 25mm² tails and a 16mm² earth for meter connections in the 80's I don't know what the other EB's around the country required at the time but it would seem likely they had the same requirements.
Since the privatisation changes to the electricity supply industry I'm not sure who specifies the size of tails required for a meter connection as the DNO's who replaced the Electricity Boards don't fit meters anymore
 

Reply to Why Are Incoming Live/Neutral 16mm and Tails From Consumer Unit 25mm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
360
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Hi I wonder if anyone has any useful thoughts on this. Client wants me to redo consumer unit but doesn’t want disruption to fabric of building...
Replies
27
Views
3K
In the UK, It is said that the neutral wire is connected to ground/earth wire along the way back to the substation. Ive inherited a setup where...
Replies
4
Views
1K
Hi First post and I'm a DIY-er so apologies if this is the wrong forum to start with. I have a project at the moment that involves replacing a...
Replies
50
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock