Discuss Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

swaRRR

Esteemed
Reaction score
266
OSG Pg.40 says:

'[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault protection of the single-insulated conductors that connect the load side of the double-pole main switch to the supply-side of the RCCB's.'

Why is there insufficient fault protection here?

I've seen loads of TT systems with RCD protection in them. What would you use instead? I know you can use RCBO's but they're not standard.
 
OSG Pg.40 says:

'[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault protection of the single-insulated conductors that connect the load side of the double-pole main switch to the supply-side of the RCCB's.'

Why is there insufficient fault protection here?

I've seen loads of TT systems with RCD protection in them. What would you use instead? I know you can use RCBO's but they're not standard
I think it's because of the split cu. The cable connecting from the bottom of the main switch to the top of the RCCB's aren't RCD protected.
If you have an RCD main switch or Isolator the it's ok.
That's my interpretation of it anyway, I may well be wrong.
 
OSG Pg.40 says:

'[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault protection of the single-insulated conductors that connect the load side of the double-pole main switch to the supply-side of the RCCB's.'

Why is there insufficient fault protection here?

I've seen loads of TT systems with RCD protection in them. What would you use instead? I know you can use RCBO's but they're not standard.
Typically, with a split-board consumer unit having one or more 30 mA RCDs for the final circuits, the front-end RCD would be 100 mA, type S (time-delayed) to permit selectivity between RCDs.


However, the cables from the origin of the supply to the input terminals of the RCD were a concern. This was because RCDs don’t protect the cables which supply their input terminals. This means that a line to earth fault on the supply side of the front-end RCD could go undetected.

Where a metal consumer unit is installed, there’s always the risk, however small, that the metal enclosure – and other exposed-conductive-parts – will make contact with a live conductor, causing the metalwork to rise to a potential approaching that of the line voltage of the supply.


The relatively high external earth loop impedance in TT systems might mean that the service cut-out fuse would not operate within the maximum permitted time of five seconds, permitting a dangerously high potential to remain on all the earthed metalwork of the installation.

Consequently, you needed to be sure that any exposed metalwork couldn’t be made live by a fault ‘before’ the RCD, caused either by an insulation fault or by one of the conductors becoming loose.
 
Last edited:
Typically, with a split-board consumer unit having one or more 30 mA RCDs for the final circuits, the front-end RCD would be 100 mA, type S (time-delayed) to permit selectivity between RCDs.


However, the cables from the origin of the supply to the input terminals of the RCD were a concern. This was because RCDs don’t protect the cables which supply their input terminals. This means that a line to earth fault on the supply side of the front-end RCD could go undetected.

Where a metal consumer unit is installed, there’s always the risk, however small, that the metal enclosure – and other exposed-conductive-parts – will make contact with a live conductor, causing the metalwork to rise to a potential approaching that of the line voltage of the supply.


The relatively high external earth loop impedance in TT systems might mean that the service cut-out fuse would not operate within the maximum permitted time of five seconds, permitting a dangerously high potential to remain on all the earthed metalwork of the installation.

Consequently, you needed to be sure that any exposed metalwork couldn’t be made live by a fault ‘before’ the RCD, caused either by an insulation fault or by one of the conductors becoming loose.
Ok but how is this different with RCBO's?

And what's the difference between a normal 100a main switch in a CU and an S Type RCD?

It's amazing how many of these i've worked on without knowing anything about them.
 
Last edited:
They are standard for me, and plenty of other sparks. I will not install a split load board anymore, as the RCBO boards are so much cheaper to buy now, and are infinitely superior.

The only sparks to be fitting them now are the John Wayne ones.

The likes of screw fix and tool station still punting them out cheap as chips type AC rcds no spd they should be ashamed.

I like the Fusebox range.
 
The only sparks to be fitting them now are the John Wayne ones.

The likes of screw fix and tool station still punting them out cheap as chips type AC rcds no spd they should be ashamed.

I like the Fusebox range.
I worked on a 1700-home council refit earlier this year where every single board was split RCD.

I also worked on several premium new builds (you know the ones where they use nice insulation instead of the stuff that itches and it comes with triple-glazing?) that used them too.

Scandalous really.
 
Not looked at an OSG for over 20 years your book of choice is BS7671.
I know that but OSG is supposed to be a bite-sized, easy reference for whats in the big brown book. Seems like the OSG talks a lot of gibberish.

Here's another one.

OSG page 61.

'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'

This basically says all breakers have to be double pole in a TT, no?

Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.
 

Reply to Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
887

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock