Went to a job today to try and rectify a fault on a ring circuit.
I visited the property some time ago and noticed the main ring was not RCD protected on a 17th ed high integrity board that had been very recently installed. I assumed a fault was present. No paperwork...
I disconnected all loads, tested,split traced etc until I discovered it was a leg in the kitchen that was most likely a three way joint that fed the boiler too, a pain as the boiler would need re supplying and the ring splitting and derating to 20A or so.
The thing was though that the fault was between L & N (0.01 M ohms). L - E, N - E 500 M ohm or so. I tried to put the circuit on the RCD as a minimum (customer wasn't prepared to pay at that time for what I wanted to do above) and the RCD would trip when operating a light switch (same RCD) or a piece of equipment. Why is this?
Also what dangers are exactly present with a poor IR reading?
Thanks
Dave
I visited the property some time ago and noticed the main ring was not RCD protected on a 17th ed high integrity board that had been very recently installed. I assumed a fault was present. No paperwork...
I disconnected all loads, tested,split traced etc until I discovered it was a leg in the kitchen that was most likely a three way joint that fed the boiler too, a pain as the boiler would need re supplying and the ring splitting and derating to 20A or so.
The thing was though that the fault was between L & N (0.01 M ohms). L - E, N - E 500 M ohm or so. I tried to put the circuit on the RCD as a minimum (customer wasn't prepared to pay at that time for what I wanted to do above) and the RCD would trip when operating a light switch (same RCD) or a piece of equipment. Why is this?
Also what dangers are exactly present with a poor IR reading?
Thanks
Dave