HI folks, I have a bit of a problem that it’d like some opinions on. I have a small wind turbine installed that the DNO will not allow on their system, this is because the metal tower and the main earth are connected together. The customers property is supplied by a TN-C-S system, so I guess I can see their point as they don’t want a lightening strike to be channelled down the PME. My belief is that we need to bond the Generator (exposed conductive part)and the tower (extraneous conductive part) together as an engineer will almost certainly come into contact with both the tower and the generator at the same time.
My proposed solution would be to not use the property earth(PME) and put the Turbine on it’s own TT system. So, sink a dedicated earthing rod at the tower and connect the tower metal work and electrical system main earth to the earth rod and put in a 4 pole RCD (the turbine is three phase and neutral).
Does this seem like a reasonable solution? Is there something here I haven’t considered? If a TT system is the correct solution them I have a question about the implementation.
My feeling is that it would be best to connect the turbine SWA cable’s armour to the property earth and ensure its insulated at the turbine so no-one can come into contact with it and the TT earth simultaneously, then have the RCD protection at the supply end of the SWA that’s supplying the turbine.
I have practically no TT system experience so any comments or feedback will be gratefully received.
Thanks in advance.
Del
My proposed solution would be to not use the property earth(PME) and put the Turbine on it’s own TT system. So, sink a dedicated earthing rod at the tower and connect the tower metal work and electrical system main earth to the earth rod and put in a 4 pole RCD (the turbine is three phase and neutral).
Does this seem like a reasonable solution? Is there something here I haven’t considered? If a TT system is the correct solution them I have a question about the implementation.
My feeling is that it would be best to connect the turbine SWA cable’s armour to the property earth and ensure its insulated at the turbine so no-one can come into contact with it and the TT earth simultaneously, then have the RCD protection at the supply end of the SWA that’s supplying the turbine.
I have practically no TT system experience so any comments or feedback will be gratefully received.
Thanks in advance.