HI folks, I have a bit of a problem that it’d like some opinions on. I have a small wind turbine installed that the DNO will not allow on their system, this is because the metal tower and the main earth are connected together. The customers property is supplied by a TN-C-S system, so I guess I can see their point as they don’t want a lightening strike to be channelled down the PME. My belief is that we need to bond the Generator (exposed conductive part)and the tower (extraneous conductive part) together as an engineer will almost certainly come into contact with both the tower and the generator at the same time.

My proposed solution would be to not use the property earth(PME) and put the Turbine on it’s own TT system. So, sink a dedicated earthing rod at the tower and connect the tower metal work and electrical system main earth to the earth rod and put in a 4 pole RCD (the turbine is three phase and neutral).

Does this seem like a reasonable solution? Is there something here I haven’t considered? If a TT system is the correct solution them I have a question about the implementation.

My feeling is that it would be best to connect the turbine SWA cable’s armour to the property earth and ensure its insulated at the turbine so no-one can come into contact with it and the TT earth simultaneously, then have the RCD protection at the supply end of the SWA that’s supplying the turbine.

I have practically no TT system experience so any comments or feedback will be gratefully received.

Thanks in advance.

Del
 
Big thanks to both of you for your responses.

The box that the supply cable goes to is plastic, but if I use a standard gland on the turbine end of the SWA then I'll bring the property earth into the same box as my seperated earth bar. Would I not be better to bring the SWA through a stuffing gland and heatshrinking the end of the armour?

Also I still can't quite get my head round wether I should have the RCD in the property or at the turbine end. I'm sure someone once said to me the RCD should go at the turbine (actually it was a garage in their TT example) but I think it would be better in the property, that way it's protecting the turbine and the cable and is also more easily accessed for testing.

Any thoughts anyone?

Thanks

Del
 
Last edited by a moderator:
The one we done in Norfolk had to be a TT as the property was on TNCS however the turbine installer and manufacture required the stake to be no higher that 10ohms. We had to get trenches dug and laid copper band until we got the reading down. You may find the manufacture has a maximum value and it will not be very high.
 

Reply to Wind Turbine Bonding With LP in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
653
And now for something completely different! I have been after a power station telegraph for decades and due to the fact most would have been...
Replies
7
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
518
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock