Is each line in the diagram a core of the T&E or the whole T&E?
If it replaced an existing switch, then the most likely is that you have a permanent live in, then the switched line return to the light.
The original switch (depending on how old) probably didn't have a neutral at the switch, so if you are feeding those new lights from the switch directly with neutrals it won't work, you'll need to take the neutral from the original light (or whatever replaced it) to the new fittings.
Then you would have the incoming permanent live from each side into the COM on the corresponding switch terminal, and the other switched lives leaving into the L1 terminal. (Or possibly L2, depending on the switch and which one is used for 1 way switching - but not both)
If there are neutrals coming in and going out, then they should be connected together behind the switch in a suitable Wago connector or similar.