Discuss Wiring Hot Tub in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
H
hutch6447
Hi been over to view job and its a 3 wire configuration for the hot tub which is already wired in, now the customer say's it keeps tripping when I looked the hot tub was wired into the garage consumer unit.
Now I have limited experience on hot tubs but I thought it had to go on its own circuit and have a gfci circuit breaker to stop false tripping but as I said this is just wired into garage consumer unit, customer said it worked for a while but now constantly trips.
I have had a look around and there are no loose connections or shorts going on.
Has anyone got experience that would help?
What do you mean by ''3 Wire Configuration'' and are you saying that the hot tub is presently without any RCD protection??? Oh ....And what is actually tripping??
Yes it is RCD protected sorry just called it that because of the info about it on net, its the circuit breaker that is tripping. Has anyone got a wiring diagram for a typical British hot tub and could it be the heating motor that is tripping it?
If it is the MCB Or circuit breaker you refer and not an rcd then it would appear to be over current. There are a few things that may be the reason but all of which do require a test meter of some description to make a diagnosis. sounds like time for ringing a local sparks to give it a going over for you.
Edit
Just seen your post as a sparks. don't understand why your asking this.
Well, if it is RCD protected and it is the circuit breaker that is tripping then it leads me to overloading or L-N short circuit.
Yeah cable is 6mm cable and its on a 20A breaker, know cable will easily take a 32a MCB its wired into the garage consumer unit which has its own rcd ( this gfci ******** was on all the instructions and downloads he gave me.
Going to run a dedicated circuit in 6mm cable there is a spare way at the main board so it will be rcd protected and put on a 32 amp Mcb but before this is there anyway that the hot tub can be tested to see if it is the heating element that is tripping it?
Well, does it trip straight away? Can you switch off the heaters, does it still trip? Can you switch off the pump, does it still trip? If that is so then ckeck the supply cable, as Lenny suspects a dead short circuit, this might very well be the case.
I cant help but feel you are short changing us with info here.
Do you have the manufacturers instructions that accompanied the hot tub???
If so does it give the maximum design current current for the hot tub and does it recommend an overcurrent device for it??? Does the currently installed device match up to requirements??? Is it infact the RCD (GFCI) that trips???
Can you shed a bit more light please.
Did some of these hot tub not require their own TT putting in as well?
Measuring the resistance of the heater and clamping it if need be may shed light.
Your saying a three wire system do you mean the supply to it (inc earth) or the feed splits into two live feeds with a shared nuetral (making3)
Hard water, the friendly hot tub repair man suggests Calgon:wink5: seriously, probably corroded to death, causing a short circuit to earth.
Reply to Wiring Hot Tub in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hi, My hot tub keeps tripping after 12 years of use. I'm thinking it's the GFCI gone bad. Unfortunately it's a CH 2 pole 50 amp (GFTCB250) and...
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
