Spent yesterday morning running a spur in my kitchen from one double socket on the rfc to a new one along the same wall.

Original socket is just beside the multi gang grid switch for appliances. More on that later.

Wife came home from shopping with the birthday girl, ranted at me for not doing any dishes, as is typical, and proceeded to fill the dishwasher…. Which didn’t work.

Got the tools out again and started looking.

The original socket and spur both tested fine with 2 prong voltage detector first, then with ELI tester. 244v, but the socket for the dishwasher although also read 244, it wasn’t lighting up the 240 light on the 2 prong.
Was also giving a warning light on the ELI as power between N and PE.

Healthy would be
L to N yes
L to PE yes
N to E no

This surprised me as every other point on the same circuit was ok.

So although I hadn’t worked on it, I deduced the only solution was to look in the grid switch plate.
Lo and behold, pulled the grid forward and not one, but two neutrals popped out… the two legs from the ring on each end.

So, dishes done, and I’m back in the good books.



Although.

They went all the way to the Metrocentre and didn’t buy me anything!
 
Last edited:
Doing stuff at home is always fraught with unexpected difficulties...
My washing machine, 2 years old, stopped working last week. It was fine in the morning, but when I put another load in that afternoon, nothing...pressed the switch and absolutely nothing at all. The Panel remained blank. I checked all the usual stuff, the fuse, the socket etc, had to drag it out of position...and it's still sitting in the middle of the kitchen floor awaiting a visit from the "engineer" on Wednesday. I did wonder if there's maybe a fuse fitted internally, but frankly can't be bothered taking out the numerous screws to remove the cover.
 
Well, that’s what I thought at first. Fuse in plug, or dishwasher fault… it’s got a really soft button as the on/off and I can see that failing eventually.

I’ve seen those grid switches fail in the past as well, and you end up needing to replace all of them and they’re not easy to work on with you head banging off a wall unit.

I hate it when a one hour job turns into an evening of fault finding.
 

Reply to Working in your own gaff when things don’t go to plan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock