Malsford

Hi
I need help in the design of a 50kW PV system, 3 phase inverter so 50000W divided by 400V = 125A. 125A divided by the square root of 3 (1.732) =72.17A per phase. is this right?
 
Why am I laughing?? I should be bawling (great industry, good prospects, helping country out of recession... shafted by the sh*ts in suits again)
 
Sounds about right. I'd put your pen down if I were you though. You may as well be designing a saddle for a unicorn.

Too late jobs already started, ive just become the installations manager and been thrown in at the deep end. job should be finished within 3 weeks
 
What are you talking about? ****s in suits? explain
I am (ithink) a good sparks whos been given a good chance to manage the installs of a bigger company than mine and took it. ive done quite a few installs with my own company but never anything this size with a 3 phase inverter.
i thought maybe i could get some good advice from this forum
 
Sorry Malsford, I didn't mean to be flippant and I'm sorry if it appeared that way.

We are all a bit shell shocked by the recent FITs news, thats all.

The reason I suggested putting your pen down is that I assumed that you were at the design stage of a 50kWp install. You're right with your sums but I am surprised that this information hasn't already been put together for the DNO. I'm assuming that the DNO have approved the install and that planning permission has been granted. If they haven't then you have less than no chance of getting it done in three weeks.
 

Reply to Working out AC on a 50kW array in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
1K
hi guys i'm trying to get my head round the following setup growatt TL3 5kW 3 phase string inverter 14 panels @ 395W Spa3000 TL ac coupled...
Replies
1
Views
704
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
472

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock