am i right we have an office area of 20m2 so we calculate the number of fittings times there lumen output which in our case is 2700 lumens times 6 = 16200 divided by 20 = 810 lux have i done this properly
 
doing a bit of googling ive notiched 2 other values must be added to the calculation cu of 0.6 and llf of o.8 so my new calculation would be 2700 x 6 x0.6 x 0.8 divided by 20m2 = 388lux that seems better any lighting experts out there lol
 
Hi mate, how many office do you have to light?

Anstel & others offer a free lighting plan when you call a rep out .

I have a large lighting plan here for a factory & offices.... I can email it you so you can look through it, it has all the cals , lux levels etc .
 
As said get a lighting rep to spec your room plan for you. The calculations are extremely complex for multiple fittings and are best done with software. You would need to include ceiling heights, angles and distances to work planes, available natural light levels, the reflective capacity of the walls etc etc.
As a very general rule of thumb, at average ceiling heights for offices, plan for two grid tiles in from the wall to a fitting, and 3 tiles max between any 2 fittings. This only works with a grid ceiling of course.. lol.
 
thanks for help guys they dont think like that were i work sort of make it up as they go along changing lots of these 600 x 600 to led types now people are complaining there to bright in office areas i have suggested your ideas to them falls on deaf ears there blaming the white walls now saying the light reflects of them even painted a couple of walls grey been in with are lux meter not saying how accurate that is but the meter is reading 800 lux in some offices were there ment to read 500 lux ive suggested removing a couple of fittings lol awiting my reply
 

Reply to working out lighting levels in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
463
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
670
Whilst having some building work done we discovered a stone lined well under our new kitchen floor , It is 25' deep and hand dug (through shillet)...
Replies
14
Views
2K
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
713

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock