I was doing a bunch of very dull office pat testing yesterday, 90% IT so hardly anything to do. It suddenly occured to me that as I could see everything bit of kit fully to be able to verify the visual condition, and I knew eveything was operable, if I just tested the via the plug on the end of each 6 way extension that they were all hanging from, I could effectively do 3 whole machines with one push of the button. I didn't, but I could have.

Right or wrong?
 
Aico 3000
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
O

oldtimer

Well you are meant to test seperate items but as I have said before clarification is need as we have "PAT" testers who cannot explain how a class II equipment test is done ie the tester shorts out the L&N so what is it referencing to ? as they say I just set the tester to class II and push the button to be honest I thought the H&S review would give us some answers but instead it was a sabre rattling exercise to contain the PAT companies who were out of control. Whether you are right or wrong does not matter as you are the one who signs that you have done it as per the COPs
 
M

moospark

Did a call centre last year, about 2 football pitches big, over 3 floors. Started testing every lead individually, no chance. test in batches I think is o.k. Obviously any batch comes in low then start going individual, I spent 9 weeks on that job, back shift, in bloody Sunderland ! How many fails? 1! and that was visual because some one had slammed a door over a lead. still it paid canny at a thin time......
 
O

oldtimer

I dont envy you I do PAT testing as part of my business and it works out to be 20 items a month and thats enough for me but 9 weeks naa no thanks
 
Last edited by a moderator:
darkwood

darkwood

Mod
Mentor
Esteemed
Arms
I cant see how you could do it this way as test sheets have earth bond resistance tests, functional load tests with leakage and sub-leakage columns which require a value not a tick or cross, multi-testing as you suggest would give false readings, i also have a software package that graphs out results and compares the reading from previous years so as to highlight trends in insulation breakdown and earthing issues which may still pass but show a impending failure.
Its an area where i feel you can't really cut corners or your results wont be true and as your recording ohms and M-ohms values it can only be done 1 item at a time.
 
trev

trev

-
Did a call centre last year, about 2 football pitches big, over 3 floors. Started testing every lead individually, no chance. test in batches I think is o.k. Obviously any batch comes in low then start going individual, I spent 9 weeks on that job, back shift, in bloody Sunderland ! How many fails? 1! and that was visual because some one had slammed a door over a lead. still it paid canny at a thin time......
9 Weeks pat testing on back shift in Sunderland?
Could life get any worse? At least you're done with it now mate:)
 
darkwood

darkwood

Mod
Mentor
Esteemed
Arms
also to consider is your tester will do an earth bond test if you have multiple items plugged in and parallel paths its possible to miss an item that failed as it won't be seen by the tester.
 
Rockingit

Rockingit

-
Mentor
Esteemed
Arms
  • Thread Starter Thread Starter
  • #9
Maybe I should have clarified - because I do so little PAT testing (got the cert, btw) I only ever use my MFT for testing as it's just not worth my while to buy a dedicated tester - so you know when you do an IR L/N > E that it's going to get everything commoned together.

I admire the concept behind tracking and graphs and things - but honestly tell me, what customer is really interested? They're just interested in a green sticker showing on every plug top.
 
O

oldtimer

I use to say soory its not worth me doing it but it started to affect the business so I tooled up and so far it will pay for its self in the first year although now that I am into it I despair with all the smoke and mirrors that surround it and by just how little guys who have been doing it for years know about it
 
M

moospark

All I.T class 2, so I.R. and visual only really, no earth bond test and sealed plugs, I could so easily have just stickered the lot, but I didn't. When I did the 2377, there was a bloke going out to Afganistan (non spark) his point was it would be pretty bad to dodge bullets all day, and then get fried sticking some toast on. Sure I.T. a bit daft 'cos you are testing at 250v which is pretty much operating current, but on a building site? yeah, you have a duty to do it right. Still laugh every time I see level 3 on that cert though!
Yes Trev. I am a Geordie, I dont have to tell you how hard.
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Reply to Would this have been allowed? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Thread starter Similar threads Forum Replies Date
M Electrical Testing & PAT Testing Forum 9
Top Bottom