Hi All,
I'm new here. I searched for existing answers to this question but did not find an answer.
I was doing some sound-proofing DIY in a one room at home and pulled-in some cable to replace old 1960's cable.
Now that I've sealed all the walls and floor and turned my attention to wiring in the sockets I discovered that I've pulled-in the wrong cable - 5 core 0.75mm heating cable :(
wiring2.JPG

I pulled-in the above 5-core 0.75 heating cable. I thought it was the type 3-core one below!

Since this is for my own house and all the floors, walls are now sealed and I cannot pull the old wires out - I've tried - am I screwed?
I was thinking that since there is just one (bedroom) socket about 5m from the main ring, I could get away with it. What do you knowledgeable people think?
 
It will need replaced. That also appears to be flex which I wouldn't be using for fixed wiring such as sockets.

It also says your from Manchester but your flag is Ireland. If you are doing this work in the free state you will need to be appropriately qualified to do so.
 
I was thinking that since there is just one (bedroom) socket about 5m from the main ring, I could get away with it. What do you knowledgeable people think?

The short answer is no way should you use the 0.75mm cable

The minimum allowed for power wiring is 1.5mm CSA as a single conductor protected by a 13A fused connection unit. Without a proper ring you would also have to drop the breaker rating to no more than 20A to protect what would be a 2.5mm radial circuit.

Without wanting to come across as provocative, can I ask why you chose to use round flexible cable instead of the normal '6242Y' twin & earth type?

T&E is generally cheaper (if of similar quality) and the thicker strands of copper are more reliable for screw connections. If I use thin stranded flexible wire (such as "tri-rated switchgear") then I normally fit crimp ferrules so the screws have something solid to bite on.
 
if this is just to feed 1 socket, do without it.
 
Also please tell us you have some plan for proper testing?

If, as I suspect, you don't have any of the typical sparks' test kit then you can hire a multi-function tester for well under £100/week, for example:


That gives you enough time to learn how to use it for basic stuff. Also you might want to get a copy of some book on testing, the usual point of reference are the IET's books, simply search for "IET guidance note 3" as a start.
 
I noticed on the 2.5mm flex you have written 34A. This cable is not fit for 34 Amps

It will be 20A or 32A if wired in a ring. But to be honest it's not really the right cable.
 
The short answer is no way should you use the 0.75mm cable

The minimum allowed for power wiring is 1.5mm CSA as a single conductor protected by a 13A fused connection unit. Without a proper ring you would also have to drop the breaker rating to no more than 20A to protect what would be a 2.5mm radial circuit.

I'm replacing an old spur socket taken from the ring

Without wanting to come across as provocative, can I ask why you chose to use round flexible cable instead of the normal '6242Y' twin & earth type?
Thanks for the reply. I thought it might make it easier to use the existing round cable as a draw-string for the new. As it is being pulled through holes in joists, I thought the 6242Y would kink easier and get stuck.
[automerge]1584651433[/automerge]
I noticed on the 2.5mm flex you have written 34A. This cable is not fit for 34 Amps

It will be 20A or 32A if wired in a ring. But to be honest it's not really the right cable.
The part number is 3-core 2.5mm Dikkan H05vv-f. The manufacturers specs say 34A and 300/500V
[automerge]1584651665[/automerge]
It will need replaced. That also appears to be flex which I wouldn't be using for fixed wiring such as sockets.

It also says your from Manchester but your flag is Ireland. If you are doing this work in the free state you will need to be appropriately qualified to do so.
Correct on part one - Internet obfuscation is the rule!, wrong on part two. It's neither controller nor restricted works so no certificate needs to be issued.
[automerge]1584652439[/automerge]
Also please tell us you have some plan for proper testing?

If, as I suspect, you don't have any of the typical sparks' test kit then you can hire a multi-function tester for well under £100/week, for example:


That gives you enough time to learn how to use it for basic stuff. Also you might want to get a copy of some book on testing, the usual point of reference are the IET's books, simply search for "IET guidance note 3" as a start.
Thanks, I will read those testing guidelines as you suggest.
 
Last edited:
It's neither controller nor restricted works so no certificate needs to be issued.
But there are numerous considerations, such as the fact that it is prohibited to have a joint in a flex. Also T&E must comply with I.S. 201-4. Even if the works are not Controlled or Restricted they must still comply with ET101:2008 (and from 1st April can be to I.S. 10101:2020).

But it's hard to state definitively that it's not Controlled or Restricted Works (i.e. Minor Works) without knowing what precisely is being done. Be warned that very, very little falls within the definition of Minor Works.
 
I'm replacing an old spur socket taken from the ring


Thanks for the reply. I thought it might make it easier to use the existing round cable as a draw-string for the new. As it is being pulled through holes in joists, I thought the 6242Y would kink easier and get stuck.
[automerge]1584651433[/automerge]

The part number is 3-core 2.5mm Dikkan H05vv-f. The manufacturers specs say 34A and 300/500V
[automerge]1584651665[/automerge]

Correct on part one - Internet obfuscation is the rule!, wrong on part two. It's neither controller nor restricted works so no certificate needs to be issued.
[automerge]1584652439[/automerge]

Thanks, I will read those testing guidelines as you suggest.
But there are numerous considerations, such as the fact that it is prohibited to have a joint in a flex. Also T&E must comply with I.S. 201-4. Even if the works are not Controlled or Restricted they must still comply with ET101:2008 (and from 1st April can be to I.S. 10101:2020).

But it's hard to state definitively that it's not Controlled or Restricted Works (i.e. Minor Works) without knowing what precisely is being done. Be warned that very, very little falls within the definition of Minor Works.
I think it is time to wish the OP good luck in his endeavours and bid him farewell.
 
I agree I would leave him to it. He doesn't seem particularly bothered about doing a decent job or listening to advice.
 

Reply to wrong wiring question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
651
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
397
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
787
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock