Long story short I ordered the "wrong" cable.... wanted H6241Y but mistakenly bought H6241B

Now, rather than faff with sending it back, I believe I can still use it but want to check with the pros. Its for a domestic lighting circuit that is currently run with live/earth loop to the switches and neutral loop at the fittings.

Given H6241Y is 1mm/PVC/70c max temp and H6241B is 1.5mm/XPLE/90c max temp I would have thought its absolutely fine to use (if anything I've paid an unnecessary premium for what I actually need).

Aside from the potential future "confusion" with the white sheath, any views on if I can use it?
 
Can't see an issue myself. The other difference is Table 4D5 vs Table 4E2 but I think that is the correct way around, the CCC being higher with what you have.
 
Can't see an issue myself. The other difference is Table 4D5 vs Table 4E2 but I think that is the correct way around, the CCC being higher with what you have.
Thanks Tim. Was also looking at Table E5 and at the 1.5m solid point there appears negligible difference between BS6004 and BS7211 cable factors too. As you say, it would be the other direction that would clearly be an issue if it was being undersized to a significant degree.

That said, I'm wondering if Table C1 comes into play.. where it says BS7211 is for use in conduits/cable ducting or trunking and BS6004 can be embedded in plaster. Since I was planning to clip direct and plaster over, does C1 prohibit it or just not include in its advisory. I'm not sure why BS7211 couldn't be embedded in plaster from a visual comparison of it.
 
Sleep easy buddy, no problems at all using this. We have to actually use this cables in schools due to Low Fume & Smoke emission, NO problem being buried in walls in the normal manner - My view is in the case of a fire, the fumes of the cables are the least of concern, where you have classrooms full of Plastic Chairs, Plastic Boxes, Plastic Storage Trays, Plastic Blinds, Plastic Paper Folders etc etc!
 
Sleep easy buddy, no problems at all using this. We have to actually use this cables in schools due to Low Fume & Smoke emission, NO problem being buried in walls in the normal manner - My view is in the case of a fire, the fumes of the cables are the least of concern, where you have classrooms full of Plastic Chairs, Plastic Boxes, Plastic Storage Trays, Plastic Blinds, Plastic Paper Folders etc etc!
Haha good point well made!
 

Reply to XLPE vs PVC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm repurposing an agricultural building as a research workshop, where sometimes reasonably accurate air temperature control will be needed. I...
Replies
7
Views
2K
P
I understand that XLPE cables operate at a maximum temperature of 90c compared with 70c for PVC insulation. What I don't understand is why the...
Replies
9
Views
9K
We recently had a thread or two about some cables that were almost certainly tinned copper, but people continued to suspect they were aluminium...
Replies
7
Views
2K
Hi all. I just repaired some damage in a commercial kitchen which frankly I was shocked by. Not literally, of course... I may treat you to some...
Replies
11
Views
7K
B
Have been concerned about an install thats running on the warm side. MCCB is rated at 200 250A supply cable is supposed to be 95mm swa (4 Core)...
Replies
25
Views
10K
baldsparkies
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock