Called around to recce a job coming up soon for a builder. Looks around house (unoccupied - nice one) things looking good for the extension. Takes a look at at existing bonding cu and supply etc. Noted the clamp on the lead covered incomer, thought thats naughty, and it was 10mm. then followed it up the cu and noticed its chopped. Ahhhh no earth, runs back to van gets tester out.

Then I go to take the lid off and notice 2 rcds, eyesight a bit sh1te but it was 100ma and 30 ma,, ok all the signs now point to TT. checks these 2 x 10mm one was to gas and water continuous bond. the other to a spike. Result Get up ye dancer.

Ze was at 0.18ohms happy with that, and better when it goes to 16mm.

But on a side note why was there a clamp on the supply incomer, I did actually test the lead sheath also to confirm earth path, but there was none. I understand why it was chopped due to twig in garage floor.

But why the use of the clamp in this instance, someone just trying to bond the cable also ??
 
around here there are quite a few houses built in the 70's with TN-S clamps on incoming sheath and a rod. could be the same, but you have a cable cut.
 
yer the 10mm from the clamp to cu was cut just below entry to cu. It seems to me by my test results the sheath of the cable is not earthed at transfomer side, its dead. If it was TN-S and the twig was used to enhance the Ze i could understand that more.
 
try an IR test @250V between bonding cable and lead sheath. that should confirm.
 
Not quite sure what you are thinking Tel,, its probably my post misleading you slightly.

If you are on about the bond to the clamp on the lead sheath, this is a bout 18 inches away and i can physically see end to end. I did a Ze direct contact to lead sheath with my test lead.

Cheers
 
No reading with direct connection to sheath of cable.

Ive got nowt on this afternoon, think i will borrow my mates tester also, and compare the Ze.com. Take some pics also.
 
I'm thinking breakdown of suppliers TNS earth at some time in the past, DNO have refused to reinstate the earth and so a sparky came in and just converted to TT and they have just left the earthing conductor in place and just cut it below CU.
 
Probably the more feasable answer. I think i will knock on a neighbours door and try and see what arrangement they have. I have an acceptable Ze. But i am now more curious to why it is this way. LOL
 
Probably the more feasable answer. I think i will knock on a neighbours door and try and see what arrangement they have. I have an acceptable Ze. But i am now more curious to why it is this way. LOL

I think you are worrying too much!

Probably no need to speak to neighbour, but have you done test with main switch open and earthing conductor taken out of the MET to confirm Ra through your rod?
 
I think you are worrying too much!

Probably no need to speak to neighbour, but have you done test with main switch open and earthing conductor taken out of the MET to confirm Ra through your rod?

not worrying at all like i said ze is acceptable. Yes i do test correctly ie switch in open position.

The problem i have is curiosity and the desire to know why things break or interprid why things are done in a particular way. Even after 30 yrs of sparking i still ask questions like an apprentice; and i still enthuse for knowledge in my chosen trade.
 
Called around to recce a job coming up soon for a builder. Looks around house (unoccupied - nice one) things looking good for the extension. Takes a look at at existing bonding cu and supply etc. Noted the clamp on the lead covered incomer, thought thats naughty, and it was 10mm. then followed it up the cu and noticed its chopped. Ahhhh no earth, runs back to van gets tester out.

Then I go to take the lid off and notice 2 rcds, eyesight a bit sh1te but it was 100ma and 30 ma,, ok all the signs now point to TT. checks these 2 x 10mm one was to gas and water continuous bond. the other to a spike. Result Get up ye dancer.

Ze was at 0.18ohms happy with that, and better when it goes to 16mm.

But on a side note why was there a clamp on the supply incomer, I did actually test the lead sheath also to confirm earth path, but there was none. I understand why it was chopped due to twig in garage floor.

But why the use of the clamp in this instance, someone just trying to bond the cable also ??
do you think this will make much difference on a TT?
;)
 
something smells wrong here. i can't see a Ze of 0.18 on a twig, TBH, even if eng54 istalled it. LOL.
 
do you think this will make much difference on a TT?
;)
Not over the distance of 2 mtrs no. However there is nothing wrong in striving to get the best reading possible on a TT. Hence more arguments on here accepting anything under 200ohms is fine.

something smells wrong here. i can't see a Ze of 0.18 on a twig, TBH, even if eng54 istalled it. LOL.
Nothing smelly here lol,why not get a good reading like that ive had a few over the years, it is what it is. Been back this afternoon, checked with another mft, and it was 0.19ohms.


it`l be parallel paths here Tel...
No parrallel paths all bonding conductors disconnected at time of testing


Thats why I asked Toonlad if he had taken the earthing conductor out of the MET.
He said he opened the main switch but not answered fully my question.
Like i said i tested it correctly. Granted i did not quote that i had removed the earth from the MET, but testing correctly is removing it,and opening the switch.


I was back this afternoon, the reading is correct, No parrallel paths the neighbours are on TT there spikes in the garage too.

so can we get back to why was there a clamp on the incomer when there is no earth path on it. The best answer has been power ranger thus far.

IMG_0343.jpg
 
Last edited:
Not over the distance of 2 mtrs no. However there is nothing wrong in striving to get the best reading possible on a TT. Hence more arguments on here accepting anything under 200ohms is fine.


Nothing smelly here lol,why not get a good reading like that ive had a few over the years, it is what it is. Been back this afternoon, checked with another mft, and it was 0.19ohms.



No parrallel paths all bonding conductors disconnected at time of testing



Like i said i tested it correctly. Granted i did not quote that i had removed the earth from the MET, but testing correctly is removing it,and opening the switch.


I was back this afternoon, the reading is correct, No parrallel paths the neighbours are on TT there spikes in the garage too.

so can we get back to why was there a clamp on the incomer when there is no earth path on it. The best answer has been power ranger thus far.

View attachment 18586
couldn`t agree with you more....depth of rod/s & suitable siting would be the key here....
 

Reply to Yesterdays little heart beat skip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K
B
Hi, My folks are just about to embark on installing a new kitchen and whilst i was round there last week i noticed that the main incoming water...
Replies
3
Views
970
So I went to do a job this morning for a builder I know. Nowt big, just extending the ring and added a few more lights. When I turned up, the...
Replies
10
Views
2K
iconnect
I
M
Hello all I'm looking for some advice please. I been out today to change a CU and when testing the 10mm water bonding I am getting a reading of...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock