Hi people

Anyone come across the issue of periodic testing shop freezer installations with YY cable fed loosely tie wrapped, direct from the DB board to plug socket units behind each freezer in the shop area
I want to C2 the installation as non standard cable, poor mechanical support and inaccessible isolation points, but I need some comfort that there is not a reasoning for justifying this type of installation as it seems to be in all stores

Any advice anyone. ?
 
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Aico 3000
davesparks

davesparks

-
Mentor
Esteemed
Arms
Can you describe the potential danger you have identified?
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
plug/socket is an acceptable form of local isolation. maybe code it C3 for the poorly installed cable.
 
Zdb

Zdb

-
Screenshot_20190603-225555_Drive.jpg

The OSG says that the use of non standard cable is "discouraged". They may as well say do what you want, we're not really that fussed:grimacing:
 
Charlie_

Charlie_

-
Arms
C3 for the issues you have described.
Is there any existing certs? With signatures for design,install & test?
Also are the sockets RCD protected?
 
Wilko

Wilko

-
Esteemed
Arms
Hi - poor mechanical support probably best judged on site. If someone were likely to trip on it or if it might be readily pulled out then perhaps C2. A few clips might turn that into a C3 for the unapproved cable.
 