Discuss Zack values in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi I was wondering if anyone could help me , I was trying to find the maximum Xs value for breakers 60947-2 and 60947-3 . Does anyone know we’re I can find this information ?
Best place would be to look up manufacturers information as they can vary.
As above . 60947-3 are just switches so do not protect from fault current. You need to know the manufacturer and make of the 60947-2 mccbs . Then go on the manufacturers web site . Where some have tables showing you the max Zs and other tech data
Reply to Zack values in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...