That wasn't clear from the op.

So I would install and test the sub main first, including live tests...

Then move on to the dead and live live tests in the new building.

You need the ze + R1 +R2 of the sub main top check the Zs of the sub main (which is also the zbd)

Then you have the zbd +R1 +R2 and then the Zs ....

So one EIC, 2 schedules ....

Where is the RCD?
Cheers Murdoch. Rcd is in main CU.
 
A separate board requires a separate test sheet and will have its own ze/z's. Zdb would not exist because the test sheet will have the board indentification information.

That's the way its always been taught at college
 
think i'll go for Zzzzzzz s. time for my morning nap.
 
A separate board requires a separate test sheet and will have its own ze/z's. Zdb would not exist because the test sheet will have the board indentification information.

That's the way its always been taught at college
It won't have its own Ze. Ze is external to the installation and therefore there can only be one.
 
I’ve left you guys to this for a few days to sort out, but I see there is still some confusion.

BS7671 requires every installation to have a Main Earth Terminal, and that every CPC and PBC within the installation shall be connected to the MET.
In the scenario I postulated there is a second installation which is supplied from the first installation.
This second installation has it’s own earthing arrangement and own MET.
As such the Earth Loop Impedance should be recorded as Ze.
However, as the second installation is supplied from the first installation and Ze has already been recorded, and similarly the Zs of the distribution circuit supplying the second installation has been recorded, Zdb is often used to avoid confusion.

If however you wish to produce two separate EICs or EICRs, or record Ze for both installations on the one EIC or EICR, that’s totally up to you.
 
However you want to spin it there’s only on ZE to an installation.
How can they be a second installation fed of the ‘first installation ‘ its one installation.
 
Now we’ll argue the definition of installation for another 4 pages -
Hobnobs or digestives with your tea?
However you want to spin it there’s only on ZE to an installation.
How can they be a second installation fed of the ‘first installation ‘ its one installation.
 

Reply to Zdb before dead tests. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
845
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
293

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock