Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.

Ze do you contact the electrical board?

And zs what would be the options?

Thanks once again

Chris
 
Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.

Ze do you contact the electrical board? only if it's a TN system

And zs what would be the options? rewire circuit in larger cable, fit a lower rated MCB,

Thanks once again

Chris

my comments in red
 
Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.

Ze do you contact the electrical board?

And zs what would be the options?

Thanks once again

Chris
If it's a TN (S/C-S) then contact the DNO to rectify (or the may say it's ok, depending on what reading it is).
If it's a TT system then you'll need to try and get the reading down.

Assuming the above are ok, then for Zs, assuming your r1 and r2 are ok (and R1+R2 is ok), either break down into separate circuits or use larger cable etc
 
So for instance if i got a ZE of 0.07 and a PFC of 3.5 KA on a 30 A BS3036, what would I need to do then? Especially if budget is at almost zero? Install rcd isolator on the tails?
 
So for instance if i got a ZE of 0.07 and a PFC of 3.5 KA on a 30 A BS3036, what would I need to do then? Especially if budget is at almost zero? Install rcd isolator on the tails?
Depends on what the suppliers fuse is in that case. The BS3036's are normally rated to 2KA max, so you are then reliant on the suppliers fuse, so probably ok. What's rcd protection got to do with this? Are you suggsting installing that to overcome the breaking limit on the BS3036's?
 
I got that impression from Marniks post someone could do that. I'm getting a bit confused. So the only way to overcome the problem would be to change the DB then? RCD is only for residual current not over current.

oops :6:
 
That the PFC at 3.5 KA is too high for the BS3036 30A Fuses.

Problem is that I have fed a 2X 32A RCBO's from the 2X BS3036 30A fuse so that the Ring main and new load cable for the cooker circuit I have added to is compliant. Some of the cables are in plastic oval at a depth less than 50mm so therefore require RCD protection.

So I put in a 4 way fuse board with just the 2 RCBO's in.

Also there fore the installation still has one point of isolation.
 
You're covered by the suppliers fuse for breaking capacity, so the problem you've to overcome is the lack of RCD protection for the cable.

to be continued in a new post ....
 

Reply to Ze and zs testing! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock