Hi there... Couple of questions for you experts. Still learning.....
Been to a factory today... It has one main incoming board and 55 distributon boards scattered around there factory...
They asked me to fit/wire a couple of socket outlets under one dist board. Which only uses the armoured of the SWA as an earth but the phase conductors are 50mm2 each and i was under the impression that you can only use the armoured strands for an earth for cable upto 25mm2 (Is this right? )
As a result i measured the Ze and it measured in at 0.99ohm, (The factory is TNS) so the maximum i can have is 0.80ohm right?
I then measured it at the incoming board and it measured 0.19ohm, which is fine.
So I phoned my boss and told him we need to run a separate earthing conductor, he told me to just take a earth off the closest steel girder and that will be good enough..
Im not convinced... Surely the DNO supplied an earth for a reason and not used rods? And would this turn the installation into TT????
Give me your expert feed back. Thanks.
Been to a factory today... It has one main incoming board and 55 distributon boards scattered around there factory...
They asked me to fit/wire a couple of socket outlets under one dist board. Which only uses the armoured of the SWA as an earth but the phase conductors are 50mm2 each and i was under the impression that you can only use the armoured strands for an earth for cable upto 25mm2 (Is this right? )
As a result i measured the Ze and it measured in at 0.99ohm, (The factory is TNS) so the maximum i can have is 0.80ohm right?
I then measured it at the incoming board and it measured 0.19ohm, which is fine.
So I phoned my boss and told him we need to run a separate earthing conductor, he told me to just take a earth off the closest steel girder and that will be good enough..
Im not convinced... Surely the DNO supplied an earth for a reason and not used rods? And would this turn the installation into TT????
Give me your expert feed back. Thanks.