ze i trying to get ze on a job but not possible to turn the power off so i want to do it by enquiry but cannot find a phone number for scottish power to help me with this problem . Any one know a phone number :confused:
To be honest, even of you find the correct phone number, they will only tell you (if you manage to get someone who knows what you are talking about) the maximum, dependent on the type of supply:
IE
PME - 0.35
TNS - 0.80
Therefore, as long as your Zs on the circuit you are working on is acceptable, then you will have put the max Ze as above, and note on the cert why you were unable to test.
just in case your asked :
regulaiton 28 page 241
distributors to provide Information : to humble electricians
if you manage to get someone your lucky they tell you the same thing out the regs
Reply to ze how do you get it by enquiry in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...
Currently I’m using freeagents platform for invoicing and it’s decent and gets the job done but it’s lacking a few features. Firstly I want to be...
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...