Discuss Ze on a SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
N
nicsin02
Hi guys, i am testing a 3-phase D/B tomorrow and its supply is only a 4-core cable so its earth comes from the Gland-frying pand and then a flying lead to the earth bar, normally doing domestic property i would disconnect earth for Ze ensuring no parralell paths, what would be the norm on this occasion? thanks guys
same procedure but measure o each of the phases. reconnect earthing conductor for PFC reading. ensure installation is isolated before dissing earth. if it's a sub-board, the EFLI is noted as Zdb
is the SWA glanded into a metal CU or an insulated one?
just remove any bonding cables.... and clip on to rail.... f its a PIR put it down as a limitation...!
if you take gland off and damage it putting it back on or damage teh strands it will be hell to fix..!
in that case, i would disconnect any bonding conductors and the fly lead. i might get shot down , but i would prefer that to the possible risk of compromising the integrity of the glanding by disconnecting . apart from the risk of having 3 live phases flopping about unglanded.
- - - Updated - - -
beaten to it by torpedo fingers. GRRRR>
must be getting old. bloody heart attack slowed me down. making a good recovery now i'm back on a few beers, though.
If this is a swa feed would this mean it is a sub-board or a feed from a switched fuse as in both cases its not a Ze but a Zdb (Zs).
Its not normal to have a swa feed in the usual sense of a supply without it going through another device.
yeah its a sub mains fed from another board, i know its a Zdb but would still have to fill it in the Ze section for the new sub board or am i wrong lol?
Actually, you're wrong.:smile:
It's Zs of the sub-main and you don't disconnect anything to measure it.
The only place you measure Ze is at the origin of the installation - and for this you disconnect the 'Earthing Conductor'.
What you are talking about disconnecting is the CPC of the SWA (Sub-main)..........and for a Zs measurement this is left connected.
If, on the other hand, your 3 phase board had it's own 'earthing system' (e.g. a seperate earth rod), then you could treat it as a seperate installation, with it's own origin and 'earthing conductor'..........then you could measure Ze at your board.
Completely agree, you will be measuring nothing but the Zs at a sub-distribution board.
At the main incoming position of that sub-board, your value can be stated as Zdb, and can be noted no doubt in the Ze position of your certificate for this sub-board, with a an explanation in the remarks column. The rest of the sub-boards circuits, will again be tested as normal for Zs values.....
Reply to Ze on a SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...