hi chaps,done a ze test on a tns supply,got a reading of 0.18 ohms.i was expecting around 0.8.can anyone shed some light on this.many thanks
 
Aico 3000 Range
This official sponsor may provide discounts for members
S

Spudnik

  • Thread Starter Thread Starter
  • #2
Did you carry out a true Ze ie with main bonds disconnected?

If so, 0.8 is the maximum, so anything under is fine.
 
S

spikey

  • Thread Starter Thread Starter
  • #3
no i didn'nt.many thanks tour a top man
 