Hi all.
Currently working on a campsite installing new hook up points. Just had a new 3 phase supply installed. Each phase feeds a separate consumer unit which in turn feeds 4double hook up points each. The supply is tncs up to the hook ups (protecting the swa) and tt at the hook ups. The ze at the hook ups varies from 240 ohms to 790 on one earth rod. Anyone got any good ideas on lowering the ze, as at the moment the rcd's aren't operating due to the high earth path I'm assuming!
Thanks
Tom
 
Sounds like you need to install multiple electrodes or else find better ground for the existing ones.
 
Additional rods/tapes/mats etc

Even at 790 ohms (which is bad) a 30mA RCD should still operate before the touch voltage threshold is exceeded. Have you tested the RCD's at all???
 
With a 30mA RCD it should be operating with an earth electrode resistance of up to 1667Ω. Ze = 50/.030. 50 is the max touch voltage. While it would be a good idea to get the Ze close to or less than 100Ω (OSG says over 200Ω may not be stable) is this the fault or is something else wrong?
 
Probably too late now but what we used to do was to strip back about 5m of 25mm green/yellow and bury it in the trenches with the swa, used to get really low Zs that way.
 
What i would do is install a rod at each hook up , or as sintra has stated use multiple Rods ,realistically and has been mentioned the readings should be less that 200 ohms for stability ,see if there are any damper area's some where that doesnt catch the sun to much happer a rod in and do an earth rod test to see what the conductivity is
 
Use a quility earth rod which you can screw another one on so that you drive it deeper. Should lower the resistance
 
i have tested the rcd's. a few were tripping at 1 x but none seem to want to at 5 x
. came across this at a house and bashed another electrode in which did sort it. the ground is very dry and very rocky so worried it may take lots of electrodes at the higher ze hook ups.
got alot pf sorting out to do on some old hook ups that are run on 2.5mm flex on a run of 50 metres underground using the pme that was supplied on the old board!
 
The supply is tncs up to the hook ups (protecting the swa) and tt at the hook ups.
WHY
Am I missing summat or is my head not working properly???
 
The supply is tncs up to the hook ups (protecting the swa) and tt at the hook ups.
WHY
Am I missing summat or is my head not working properly???

Because it's a caravan park.
 
i mean that the pme supply protects the armoured but is not taken into the hook ups, as pme is not permitted to supply caravans. Sorry may not have explained it very well there, or is that not the way you would have done it?!
 
not sure if that reply posted then. What i mean is that the pme from the supply is used to protect the armoured cables, but it does not enter the hook up points as pme is not allowed to supply the caravans. Sorry if i didnt explain very well. Is this not the standard way of going about this then?
Thanks for all the fast replies
 
so the tncs cannot be used to protect the armoured then?! its easy to disconnect them from the supply and swap it to the tt at the hook ups, i thought that it could be used however though as its not supplying anything portable.
 

Reply to Ze on campsite in the Australia area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
472
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
992
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
519

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock