really need to see the Q. high readings can have several causes. a Zs fault seems to suggest that a reading can't be obtained.
 
unfortunately i cant remember it word for word but it was definately along the lines of.... you find a fault during a Zs test what would you do .....and my brain went blank!!!
 
The wording of the question needs to be checked Lady of Ogwr :)

Your second post seems more to the point
It may be that you have measured a high reading and are being asked what to do to find that high reading/ problem/fault

See if you can get hold of the question and post it word for word,then these good folk will do what they can to go through it with you
 
if you have a Zs fault, the circuit needs to be first isolated, then locked, as under fault conditions the circuit will not trip in the time required by BS7671.

You would need to check the circuitry for loose connections first, if none could be found, then the circuit would then require an improvement by means of a lower rated or type MCB, 20 down to 10, or C down to B etc, if this still cannot be obtained. It would need to be rewired.
 
an RCd can also be used, but in my opinion, i would rather cure the problem than the symptoms, so would rewire if possible.

i would see which of the conductors is giving the high reading. if it is the CPC, then you can use paralell paths to reduce this via trunking, tray ect. its not good practice, but is an option.
 
its what they teach you these days and reason i said that is because we were talking about the exact subject on monday. not always an option for new circuit or breaker device to be reduced, thats all folks!!!!!!!!!!!!!!!
 
had a similar problem to be solved in the 2391 practical.
Zs value was too high for ADS.
Assuming the system is TN-C-S
Number of solutions:
Check R1 +R2 equals what you would expect using the resistances/m as shown in OSG page 166. Could indicate poor connections
Check the MCB type as it could be a C type where it may be possible to have a B type depending on what the load type is. B types have a higher max Zs value compared to C's
Could reduce the length of the circuit
Could use cables for the circuit having a larger csa
 
and if all else fails there is always the fast track course 7 weeks learning how to lie through your teeth, become a .......... politician, lawyer, estate agent, salesman, banker, care home manager, any manager, sure there's more.......
 

Reply to Zs fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
637
having failed my first attempt at 18th edition exam, does anyone have any tips and tricks on how to study for the exam? being that there is a...
Replies
8
Views
806
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
972
OLDBOY
O
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
812

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock