Discuss zs testing in the UK Electrical Forum area at ElectriciansForums.net
Bonding should be, yes. What other kinds of parallel paths could there be, bearing in mind during testing anything not relevant to the testing should be disconnected?
You're saying you disconnect parallel paths apart from bonding while taking a measurement? Good luck with that outside of a 2 up 2 down!
A list of parallel paths is endless. Motor sat on a steel platform for example. Try disconnecting that while measuring Zs.
My point is, parallel paths come and go during the life of the install. The CPC is there to stay so why having a worst case scenario such a bad thing?
For example, man fits motor, motor vibrates, man fits anti vibration feet, parallel path lost, Zs increases. Disconnection time now not achieved.
I'm not saying it's better, just cannot understand some people's resistance to calculate.
The original question was about a college question, but if a Zs were likely to be increased the person likely to be increasing it should measure the Zs when he alters it.
Similar questions have come up before, and the general consensus is you can't account for alterations which may be made.
Why arse around calculating when you can directly test/measure the Zs at any given point on the circuit, and get an accurate value into the bargain!!!
Because it can be safer, but it seems we're going around in circles now.
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...
Depends on the circumstances.
Who said anything about Ze? Why would you not be able to take a live Ze reading? And how else would you take it?
There IS something very wrong with the industry unfortunately.
What if you were using metallic containment as the CPC?
Measure is the only solution.
Because it can take hours to get ISO locks taken off and reinstated.
And you can get accurate results with a brew in your hand rather then an MFT.
There IS something very wrong with the industry unfortunately. Agreed!!
Measure is the only solution. Are you having a laugh or what??
Because it can take hours to get ISO locks taken off and reinstated. So how are you going to take dead test values to calculate??
And you can get accurate results with a brew in your hand rather than an MFT.
I'll guarantee that any calculated value you come up with, will not be the same as the live measured value!!
And coupled to this new convoluted Zs measurement, where it seems you need to know the bloody voltage, even less likely... lol!!
Why is calculating Zs theoretical? You have measured the Ze and R1 R2 using a calibrated meter.
Just do the maths.
(Tin hat on) I know I'm in the minority here....
Because the maths takes no account of parallel paths and does not give the true reading.
Are all parallel paths permanent?
depends, an install we did had that much steel bolted together and that many swa cables that the results were way better than they should have been, because of the design of the building most steel work was directly connected without bonding cables
Surprised no one has mentioned the inaccuracy of 'no trip' ZS tests yet. I seldom get a measured value lower than a calculated when on 'no trip'.
A valid point that i didn't consider, as we initially temporarily install spare double pole, TP+N breakers/ isolators, only installing the RCD units at time of testing the RCD's. So i'd say 95 % of all our circuits Zs testing is carried out at full current...
Surprised that no one has mention that you can get your Ze "by enquiry" then test for Voltage, dead test R1+R2.
If the Ze = 0.17
R1+R2 = 0.54
V = 237
Only two tests needed lol
Zs = 0.17 + 0.54 = 0.71
PFC = 237 / 0.17 = 1.39kA
All the maths are thrown out of the window soon as you get the MFT out. The test results will never match the maths in the real world and should only be used as a calculated/estimate of results before testing to compare against.
With the things we have these days like socket adapters and Lightmates, no reason not to safely carry out tests.
Cant really explain it any better or clearer than this.
Firstly my apologies for interrupting a thread. I'm an avid reader of forums but not well versed with any etiquette .
I have particularly sought to seek your advice as I deeply respect your knowledge and understanding of the 2394/5 examinations.
I am undertaking the 2394 written exam in a few weeks and have been just finalising my revision notes. I have made use of the published Chief Examiners Reports which do tend to point out the basic errors students make.
However one note from a report (Aug 2014) is confusing me, and I would be grateful for your thoughts.
To quote from the report :-
"Candidates were asked to explain the expected pattern of test results when carrying out an earth fault loop impedance measurement at each socket-outlet on the ring circuit. Many candidates incorrectly believed that the results would be the same at each socket-outlet. "
Please correct me if wrong but I have been taught that a correctly installed ring circuit will have substantially the same (R1 + R2) value at each socket outlet (within 0.05ohms). The only exception would be where the ring contains a spur , the (R1 +R2) being marginally higher at this point , proportional to the extra cable length.
I have also been taught that the following calculation is used to calculate Zs , Zs = Ze + (R1 + R2). I'm fully aware of ambient temperature and conductor operating temperature considerations for verification but lets keep it simple for now. Ze is a constant, as mentioned (R1 + R2) should be substantially the same for each outlet so my question is why would it not be conceivable to expect substantially the same Zs values ?
Again my apologies for interrupting this thread, I would be really grateful for thoughts .
you're slightly confused here. when cross connecting the RFC legs, you should get R1+R2 at each outlet will be the same. your Zs readings are taken with the RFC legs connected into the supply, so will be dependent on the resistances when in this configuration. i.e, highest reading will be at thew mid point.
Now why couldn't I have thought of that much easier explanation instead of drawing this diagram!
Thank you for your reply, makes perfect sense . I will bring it to the attention of my tutor as ironically the very same question came up in a mock paper we went through before the Easter break . There were differing views as to the answer. Again, many thanks.
Reply to zs testing in the UK Electrical Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...