Evening all.

Is there a regulation or any guidance regarding live zs testing with loads connected....

Eg zs testing on a 3phase motor whilst it is running. Could the current being drawn damage the meter if testing at the end of line.... Or doing a live zdb test, is there any guidance to say there must be no live loads or a maximum current being drawn at time of test ?

I hope this makes sense I am new to testing and don't want to damage my mft1730 Megger.

Thanks
 

pc1966

Esteemed
Arms
Reaction score
6,743
The running motor won't damage your MFT but it can lead to a higher than expected PSCC as the motor has inertial and on slowing works as a generator. As a result it is not really giving you the circuit's Zs value for fault clearing at the supply, since you have in effect a 2nd power source nearby.

In some larger systems where you are trying to work out max fault currents (either for checking MCCB/fuse/switch limits, or arc-flash safety calculations) then the contributions of nearby motors can be significant, at least for a few cycles of the AC as its magnetic field collapses (or it stops, probably later).
 
Last edited:

Reply to Zs testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I...
Replies
27
Views
1K
Hi all i'm after some advice please, I was trained as a pat tester for my company a few years back (10 years)to test ex display lamps ect ect, we...
Replies
22
Views
825
We are carrying out some electrical testing on an installation. From the fuse board it supplies 415v to a transformer which is stepped down to...
Replies
7
Views
449
Good evening, 1) Is the motor current on the nameplate always the full load current: the maximum current the motor can draw without there being...
Replies
3
Views
384
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
895

New Posts (Please Reply)

Top